code question on Microwave electrical supply

stash-hdyJanuary 24, 2010

Want to add a builtin Microwave over the oven, there is not a plug in the space. There is a range hood next to it with a plug. Question can I tap into the range hood plug and run a plug for the Microwave?

Thank you for reporting this comment. Undo
petey_racer

Not unless the hood is on a dedicated circuit, which is HIGHLY unlikely.

You need to run a new circuit for it.

    Bookmark   January 24, 2010 at 2:56PM
Thank you for reporting this comment. Undo
stash-hdy

thanks, that's why I asked. The microwave draws 13.9 amps is a 15 amp circuit sufficient?

    Bookmark   January 27, 2010 at 9:53PM
Thank you for reporting this comment. Undo
petey_racer

No, install a 20A.

    Bookmark   January 27, 2010 at 11:07PM
Thank you for reporting this comment. Undo
stash-hdy

thanks, looking at my panel the slots are all filled. Can I use a double circuit breaker in a 20 Amp circuit that is already there? Are there any other considerations I need to be aware of using a double circuit breaker?

    Bookmark   January 28, 2010 at 8:05AM
Thank you for reporting this comment. Undo
normel

thanks, looking at my panel the slots are all filled. Can I use a double circuit breaker in a 20 Amp circuit that is already there? Are there any other considerations I need to be aware of using a double circuit breaker?

You need to make sure your panel will accept tandem or half-size breakers.

    Bookmark   January 28, 2010 at 9:15AM
Thank you for reporting this comment. Undo
Billl

If you don't know about your box, check for the model number. It will have something like "letters" 2, 2 digit numbers "letters and numbers" on it. The first number is the total slots in the box. The second is the total allowed unit. In 1624, you would have 16 slots and 8 of them could be used for tandem or half-size breakers. Generally, if only some of the slots accept tandem breakers, it will be the bottom slots. The panel should have a wiring diagram on it for you to confirm.

    Bookmark   January 28, 2010 at 9:52AM
Thank you for reporting this comment. Undo
mcmike4817

Where should the outlet be installed for the microwave? How High? In the cabinet above it? plug in or hard wired?
Mike

    Bookmark   February 2, 2010 at 11:26AM
Thank you for reporting this comment. Undo
petey_racer

In the cabinet above the micro; to the right side; typically low as opposed to high up; plug-in...NEVER hard wired.

    Bookmark   February 2, 2010 at 8:08PM
Thank you for reporting this comment. Undo
mcmike4817

Thanks

    Bookmark   February 2, 2010 at 9:59PM
Sign Up to comment
More Discussions
Two fans on same circuit in different rooms, can't get wiring right
So here's the situation. I have two ceiling fan/lights...
jenfarino
2 Lights Out on 4 Light Fixture
I was sitting at my dining room table, heard a tiny...
Cassandra
Wireless light switch for switched outlet?
So we have no overhead lighting in any of our bedrooms,...
vikingshelmut
Disposer Power Cord
I recently bought a GE disposal online. The model is...
africanboy
Electrical Problem.
My mom's house has a problem with the lights temporarily...
Debra Johnson
Sponsored Products
Revolution Cocktail Shaker - Fferrone Design
$200.00 | HORNE
Arteriors Home - Frigg Mirror - 2549
Great Furniture Deal
Hudson Black 28-inch to 48-inch Curtain Rod
$53.95 | Bellacor
HR-88 12V Halogen Puck Light
LBC Lighting
Soft Line Turnbuckles
Lightology
Ideal Storm Door Cat Door - PCF
$27.99 | Hayneedle
© 2015 Houzz Inc. Houzz® The new way to design your home™