I'm thinking of buying a portable induction cooktop for my home. One model uses 1800 watts. Is it going to blow fuses in my house? I'm thinking of using it in rooms other than the kitchen.

Thank you for reporting this comment. Undo
Billl

1800 watts on a 120v = 15 amps. If anything else is on, that would trip a 15amp breaker. That is the most common size for bedrooms, dining rooms etc.

    Bookmark   January 14, 2010 at 8:56AM
Thank you for reporting this comment. Undo
texasredhead

I would only use the device on 20 amp circuits in GFCI protected recepticles.

    Bookmark   January 14, 2010 at 9:36AM
Thank you for reporting this comment. Undo
hrajotte

This cooktop is a 120 volt model? Plug-in 120V heating appliances >1500 watts are unusual, but not unheard of. Some hair dryers and toasters are 1800+ watts, but these are typically used for just a few minutes at a time. I would not use this cooktop for long periods on a 15A circuit, even if there is nothing else on the circuit. Of course, if there are multiple heating elements, and you're not using them all, you should be OK on a 15A circuit even of it's used for an extended period.
Check the manual to see if a 20A circuit is required. If so, I'd expect the cooktop to have a 20A plug on the cord. I guess this would depend on whether the unit is designed for "continuous use."

    Bookmark   January 14, 2010 at 9:43AM
Thank you for reporting this comment. Undo
joed

1800watts is a rating. The device probably will never actually draw that much. If it comes with a 15 amp cord and plug then it is designed to be used on a regular cirucit. I would not be using anything alse on the circuit at the time.

    Bookmark   January 14, 2010 at 11:38AM
Thank you for reporting this comment. Undo
graywings123

Thanks for the info!

    Bookmark   January 14, 2010 at 8:14PM
Sign Up to comment
More Discussions
Garage florescent light flickering - bulb or fixture problem?
I replaced the GE F40 RES garage lights with a GE F40...
bibbus 7b
Subpanel Question
I have a 100 amp panel being fed by #4 awg copper wire I...
Calo Renovations
Goodbye Phone Jack: what to do with wires?
We want to remove this phone jack. It's in a useless...
maggiepatty
Installing 220/240V. 50/60Hz appliances from Europe
I hope to install a "Domino" modular system...
panchoandlefty
Wireless light switch for switched outlet?
So we have no overhead lighting in any of our bedrooms,...
vikingshelmut
Sponsored Products
Quest Concealed 2 Outlet Twin & Diverter Thermostatic Shower Valve
Hudson Reed
Artecnica Square Phrena Pendant Lamp
ModernistLighting.com
Hampton Bay Wall Mounted Large Wall-Mount 1-Light Outdoor Prairie Bronze
$69.97 | Home Depot
Elk Lighting Flushmounts 2 Light Flush Mount in Brushed Nickel
Beyond Stores
Savoy House Liberty Craftsman-Mission Chandelier
1800Lighting
Orion Concealed Thermostatic Triple Shower Valve & Diverter 3 Outlets
Hudson Reed
MIO Alpha Continuous Heart Rate Sports Watch
$199.00 | FRONTGATE
Asaki Multi-Bulb Pendant Lamp - Large, Includes 10 Bulbs
ModernistLighting.com
© 2015 Houzz Inc. Houzz® The new way to design your home™