This is a new problem but over the past month my lights in the house are dimming when my washing machine starts up. I have 200 amp service and my central ac doesn't dim the lights in my house. I should say that the lights dimming are not even on the same dedicated 20 amp circuit as the washer. Is the washer possibly going? Could a bad breaker cause this problem? Any advice would be appreciated.

Thank you for reporting this comment. Undo
sdello

Interesting that it affects lights that are not on the same circuit. FYI, there is a separate forum on this board for Electrical Wiring. You may have better luck posting there.

    Bookmark   August 3, 2012 at 9:20AM
Thank you for reporting this comment. Undo
bus_driver

It is doubtful that there is a real problem. I once lived where the power company transformer on the pole was too small for the load. The lights dimmed slightly in time with the washer agitator oscillations.
Motors at the instant of starting draw several times the running amperage. High amperage draw causes voltage drop. The "LRA" on the nameplate is the Locked Rotor Amps and is the same as the instantaneous draw when starting without added load. The washer mechanism plus the wet clothes is a substantial added load.
Use a plug-in voltmeter, available on eBay, in the receptacle for the washer and observe it while the washer is in use.

    Bookmark   August 3, 2012 at 10:22AM
Thank you for reporting this comment. Undo
HandyMac

Call your power company. They may have a program where they test your circuits to find loose connections(which is what your problem sounds like. A loose neutral or ground can cause that situation.

    Bookmark   August 3, 2012 at 11:56AM
Thank you for reporting this comment. Undo
ionized_gw

What do you mean by "starts up", when the valves open to fill, when it starts to agitate or when it starts to spin?

If nothing else has changed, your washing machine motor may be going out or, more likely, the brakes sticking. LIsten carefully to the washing machine. Does it sound any different?

    Bookmark   August 3, 2012 at 2:27PM
Thank you for reporting this comment. Undo
gryd

Thanks for the responses. It dims lights when it starts to agitate I believe. It doesn't sound any different than it used to but it is 10 years old.

I can call the power company but you would think that the lights would also dim when the central ac started and it doesn't.

I will also try on the electrical forum. Thanks guys!

    Bookmark   August 3, 2012 at 3:22PM
Thank you for reporting this comment. Undo
brickeyee

"you would think that the lights would also dim when the central ac started and it doesn't. "

The central AC is normally a 240 v load.

If the POCO (or your power drop) had a problem ALL the circuits the house would be affected when the AC started.

Unless you want to learn how an 'Edison circuit' (AKA 'split phase') operates it is NOT as simple as you seem to believe.

    Bookmark   August 3, 2012 at 5:39PM
Thank you for reporting this comment. Undo
Fori is not pleased

Get it checked.

I used to have all my lights throb with my vintage induction cooktop (took a lot of juice to run that thing). We didn't notice it with other appliances but they didn't have that constant on-off that makes it really obvious.

Eventually we had a little electrical fire. Forgot what it was. A bad ground in the circuit box or something simple. But yeah, fire.

So just get it checked.

    Bookmark   August 3, 2012 at 8:24PM
Thank you for reporting this comment. Undo
brickeyee

A bad ground would not cause a problem since grounds only conduct power when there is a fault.

A bad neutral (ASA the 'grounded conductor') can cause real problems.

Neutral issues almost always exhibit as brightening of some lights an dimming of others as the center point of the 120/240 V system moves around as there is not 120 V on each leg.

    Bookmark   August 4, 2012 at 3:58PM
Thank you for reporting this comment. Undo
gryd

Update:
Ran washing machine on a different circuit and house lights still dimmed and flickered. Machine does seem to struggle a bit during agitation cycle. Time to call an appliance repair person.

    Bookmark   August 5, 2012 at 7:13PM
Thank you for reporting this comment. Undo
ionized_gw

There is some good diagnostic information on appliance parts web sites. Appliancepartspros is good and so is mangemylife.com.

    Bookmark   August 5, 2012 at 8:44PM
Sign Up to comment
More Discussions
Painting exterior of house with cedar siding---what to expect
I am about to start getting estimates on having the...
sierrashopper
Curtain Rods
Hi, I am not sure where to post this so my apologies...
newquilter
Roof repair -- fair price?
Hi everyone! This is my first time posting here and...
vashts85
Metal fence panels - steel or aluminum? Best brands?
I want to put up a fence to divide my side yard from...
ktmast
Stranges lines in frost pattern on roof
I have these lines on the roof when there is a frost....
cswartzwelder
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™