richard904March 7, 2008

We have a roof leak at the flashing where a cathedral ceiling meets a vertical wall. The flashing looks like an Air Vent made Flash FilterVent which provides air flow and flashing protection. It is a clever piece. It is used to provide air flow from the soffit vents to the ridge of the ceiling. In the current literature there is a serious debate on the need for the air flow in a cathedral ceiling. Using ordinary flashing to make the repair (which would block any exhaust flow) would be much cheaper and easier. Would this be a big risk?

Thank you for reporting this comment. Undo
manhattan42

I'm not sure what 'literature' you are referring to, but ventilating rafter spaces in a cathedral ceiling is mandatory under building codes.

If you do not vent the rafter spaces, you will trap water vapor from the room below. If you do not vent the rafter spaces, your roof will be hotter than it should be.

The result of an unventilated cathedral ceiling will be the complete failure of the entire roof system and premature shingle failure.

The solution without ventilation, could result in needing the entire roof system demolished and rebuilt...I have seen it happen.

So find some way to maintain your ventilation while solving your leak problems.

    Bookmark   March 8, 2008 at 9:51AM
Thank you for reporting this comment. Undo
richard904

I now agree that a house my age (built in 1994) with a cathedral ceiling insulated with fiber glass would need to retain the venting to reduce the potential moisture problems.

The literature I was referring to was the paper by Anton TenWolde and William B. Rose, "Issues Related to Venting of Attics and Cathedral Ceilings." It is a pdf file on the web site www.fpl.fs.fed.us/documents/pdf1999/tenwo99a.pdf. Also, in researching this question there are several web sites by obviously experienced insulating people that use either dense pack cellulose or spray foam in the rafters and cite there is no need therefore to vent the cathedral ceiling since either material stops air movement and both are moisture resistant. In my case this is theoretical since I am stuck with what I have.

    Bookmark   March 8, 2008 at 9:20PM
Thank you for reporting this comment. Undo
green-zeus

Maybe you can resolve the problem by talking to some roofers. Talk to many of them--they may have a way of resolving this. At the very least, you'll get a good education by taking in many opinions, which then may help you know more about it so you can chose the best solution.

    Bookmark   March 10, 2008 at 11:14AM
Thank you for reporting this comment. Undo
kbrod7

Per 2010 IRC Code, Polyurethane spray foam insulation may be used per below:

SECTION R806 ROOF VENTILATION

R806.1 Ventilation required. Enclosed attics and enclosed rafter spaces formed where ceilings are applied directly to the underside of roof rafters shall have cross ventilation for each separate space by ventilating openings protected against the entrance of rain or snow. Ventilation openings shall have a least dimension of 1/16 inch (1.6 mm) minimum and 1/4 inch (6.4 mm) maximum. Ventilation openings having a dimension greater than 1/4 inch (6.4 mm) shall be provided with corrosion-resistant wire cloth screening, hardware cloth, or similar material with openings having a minimum dimension of 1/16 inch (1.6 mm) minimum and 1/4 inch (6.4 mm) maximum. Openings in roof framing members shall conform to the requirements of Section R802.7.

R806.2 Minimum area. The total net free ventilating area shall not be less than 1/150 of the area of the space ventilated except that reduction of the total area to 1/300 is permitted provided that at least 50 percent and not more than 80 percent of the required ventilating area is provided by ventilators located in the upper portion of the space to be ventilated at least 3 feet (914 mm) above the eave or cornice vents with the balance of the required ventilation provided by eave or cornice vents. As an alternative, the net free cross-ventilation area may be reduced to 1/300 when a Class I or II vapor barrier is installed on the warm-in-winter side of the ceiling.

R806.3 Vent and insulation clearance. Where eave or cornice vents are installed, insulation shall not block the free flow of air. A minimum of a 1-inch (25 mm) space shall be provided between the insulation and the roof sheathing and at the location of the vent.

R806.4 Unvented attic assemblies. Unvented attic assemblies (spaces between the ceiling joists of the top story and the roof rafters) shall be permitted if all the following conditions are met:

  1. The unvented attic space is completely contained within the building thermal envelope.

  2. No interior vapor retarders (Class I or II) are installed on the ceiling side (attic floor) of the unvented attic assembly.

  3. Where wood shingles or shakes are used, a minimum 1/4 inch (6 mm) vented air space separates the shingles or shakes and the roofing underlayment above the structural sheathing.

  4. In climate zones 5 and 6 any air-impermeable (eg.- spray foam) insulation shall be a Class III vapor retarder, or shall have a vapor retarder coating or covering in direct contact with the underside of the insulation.

  5. Either Items 5.1, 5.2 or 5.3 shall be met, depending on the air permeability of the insulation directly under the structural roof sheathing.

5.1. Air-impermeable (eg. spray foam) insulation only. Insulation shall be applied in direct contact with the underside of the structural roof sheathing.

5.2. Air-permeable (eg. fiberglass or cellulose) insulation only. In addition to the air-permeable insulation installed directly below the structural sheathing, rigid board sheet insulation shall be installed directly above the structural roof sheathing as specified in Table R806.4 for condensation control.

5.3. Air-impermeable and air-permeable insulation. The air-impermeable (eg. spray foam) insulation shall be applied in direct contact with the underside of the structural roof sheathing as specified in Table R806.4 for condensation control. The air-permeable (eg. fiberglass or cellulose) insulation shall be installed directly under the air-impermeable (eg. spray foam) insulation.

TABLE 806.4 INSULATION FOR CONDENSATION CONTROL

CLIMATE ZONE MINIMUM RIGID BOARD OR AIR-IMPERMEABLE INSULATION R-VALUEa
4 R-15
5 R-20
6 R-25

    Bookmark   August 22, 2012 at 1:08PM
Thank you for reporting this comment. Undo
kbrod7

Per 2010 IRC Code, Polyurethane spray foam insulation may be used in an UNVENTED roof per below:

SECTION R806 ROOF VENTILATION

R806.1 Ventilation required. Enclosed attics and enclosed rafter spaces formed where ceilings are applied directly to the underside of roof rafters shall have cross ventilation for each separate space by ventilating openings protected against the entrance of rain or snow. Ventilation openings shall have a least dimension of 1/16 inch (1.6 mm) minimum and 1/4 inch (6.4 mm) maximum. Ventilation openings having a dimension greater than 1/4 inch (6.4 mm) shall be provided with corrosion-resistant wire cloth screening, hardware cloth, or similar material with openings having a minimum dimension of 1/16 inch (1.6 mm) minimum and 1/4 inch (6.4 mm) maximum. Openings in roof framing members shall conform to the requirements of Section R802.7.

R806.2 Minimum area. The total net free ventilating area shall not be less than 1/150 of the area of the space ventilated except that reduction of the total area to 1/300 is permitted provided that at least 50 percent and not more than 80 percent of the required ventilating area is provided by ventilators located in the upper portion of the space to be ventilated at least 3 feet (914 mm) above the eave or cornice vents with the balance of the required ventilation provided by eave or cornice vents. As an alternative, the net free cross-ventilation area may be reduced to 1/300 when a Class I or II vapor barrier is installed on the warm-in-winter side of the ceiling.

R806.3 Vent and insulation clearance. Where eave or cornice vents are installed, insulation shall not block the free flow of air. A minimum of a 1-inch (25 mm) space shall be provided between the insulation and the roof sheathing and at the location of the vent.

R806.4 Unvented attic assemblies. Unvented attic assemblies (spaces between the ceiling joists of the top story and the roof rafters) shall be permitted if all the following conditions are met:

  1. The unvented attic space is completely contained within the building thermal envelope.

  2. No interior vapor retarders (Class I or II) are installed on the ceiling side (attic floor) of the unvented attic assembly.

  3. Where wood shingles or shakes are used, a minimum 1/4 inch (6 mm) vented air space separates the shingles or shakes and the roofing underlayment above the structural sheathing.

  4. In climate zones 5 and 6 any air-impermeable (eg.- spray foam) insulation shall be a Class III vapor retarder, or shall have a vapor retarder coating or covering in direct contact with the underside of the insulation.

  5. Either Items 5.1, 5.2 or 5.3 shall be met, depending on the air permeability of the insulation directly under the structural roof sheathing.

5.1. Air-impermeable (eg. spray foam) insulation only. Insulation shall be applied in direct contact with the underside of the structural roof sheathing.

5.2. Air-permeable (eg. fiberglass or cellulose) insulation only. In addition to the air-permeable insulation installed directly below the structural sheathing, rigid board sheet insulation shall be installed directly above the structural roof sheathing as specified in Table R806.4 for condensation control.

5.3. Air-impermeable and air-permeable insulation. The air-impermeable (eg. spray foam) insulation shall be applied in direct contact with the underside of the structural roof sheathing as specified in Table R806.4 for condensation control. The air-permeable (eg. fiberglass or cellulose) insulation shall be installed directly under the air-impermeable (eg. spray foam) insulation.

TABLE 806.4 INSULATION FOR CONDENSATION CONTROL

CLIMATE ZONE MINIMUM RIGID BOARD OR AIR-IMPERMEABLE INSULATION R-VALUEa
4 R-15
5 R-20
6 R-25

    Bookmark   August 22, 2012 at 1:09PM
Sign Up to comment
More Discussions
damp/ruined dry wall in window corners
I need help with a plan or how to for fixing and repairing...
betty_joanne
What type of wall is this and how do I fix it?
The bottom part of my closet interior wall is crumbling,...
sippy_spence
Settling crack been repaired by 6 people - any advice?
Our house is 25 years old. The foundation was put in...
BelfastBound
Fixing Spanish Plaster and plaster interior walls (1933 house)
We live in a 1933 Lannon stone home (Lannon stone is...
rachelep
Crawlspace floods with water, but it doesnt touch the wood, ok?
I have a crawlspace that is about 2 ft from the ground....
tlbean2004
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™