Floor structure is in question

oldhousetimeFebruary 1, 2010

Well, I am in a dilemma. Bought an old House, 1905, gutted the 2nd floor bathroom and would like to put a cast Iron tub in. The tub with water will weight about 500lbs. When ripping out the bathroom, the subfloor , which was diagonally placed 2 x 6s that went from one room to the other, have been taken out. The floor joists have large holes from old plumbing plus holes for new plumbing. I am worried that the diagonal subfloor boards did more then act as just sub flooring, but distributed weight to a larger surface making less load in the bathroom...

Can I sister the joists and call it a day or should I think about something more invasive.

This problem has been keeping us from moving forward.

Thank you in advance.

J

Thank you for reporting this comment. Undo
macv

No one can tell you what to do without seeing the situation but if joists are properly sistered they should be as strong as the original structure. Of course, you can replace the subfloor with 3/4 plywood which should be stronger than the original sub floor.

    Bookmark   February 1, 2010 at 9:07PM
Thank you for reporting this comment. Undo
brickeyee

3/4 in plywood is not even near the strength of diagonal 2x6 sub flooring.

Even 1x6 diagonal is stronger than 3/4 in plywood.

    Bookmark   February 2, 2010 at 4:02PM
Thank you for reporting this comment. Undo
macv

The plywood, installed properly, would act in compression along the top of the joist where the 1x6's would not. If replacing 2x6's then 1 1/2" of plywood would be even stronger.

Plywood would also be stronger as a subfloor because it would be the same thickness but span a shorter distance not that it would necessarily matter in this case.

    Bookmark   February 2, 2010 at 6:48PM
Thank you for reporting this comment. Undo
brickeyee

Only half the plies in perpendicular layed plywood are providing any real strength.

Solid wood acts just fine in compression and tension, with its full cross section doing work.

The reason everyone switched to plywood is for the reduced labor of installation of 4x8 sheets, not strength.

    Bookmark   February 3, 2010 at 9:46AM
Thank you for reporting this comment. Undo
Billl

I think the OP is just concerned that the floor is solid, not a debate of wood vs plywood.

Plywood is a perfectly acceptable subfloor and will provide all the strength you need as long as the underlying framing is solid. You should check the spacing on the floor joists though.

    Bookmark   February 3, 2010 at 10:21AM
Sign Up to comment
More Discussions
Removing brick and install what?
Just for the sake of discussion...if one was to remove...
mlo1
Do I match exterior door/window hardware to interior?
We will have white interior doors with oil rubbed bronze...
happyallison
Build an Addition, Move, or Stick it out?
We live in a land-locked area with high real estate prices....
neverlandpirate
Learning to read plans and drawings
We are embarking on the design phase for a remodel...
Susan Taylor Brown
"Green" Remodeling - where to start?
We would like to remodel using materials and processes...
prairiemoon2 z6 MA
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™