Pentair MiniMax NT - Blower Help

bigredpepperNovember 30, 2007

Hi,

I just replaced the Digital Display Controller (472100) on my Pentair Minimax NT spa heater. Now I get ERR on the front panel. Cycling power on the junction box gives me one red flash on the Ignition Module, which maps to Air Flow Fault.

Any suggestions on how to troubleshoot further?

The blower never comes on, I suspect the blower but have no idea how to confirm.

Manual w/ wiring diagram here:

http://www.pool-heaters.com/pdf/MiniMax-NT-Electronic-manual.pdf

Thanks in advance,

Any help in avoiding the pool/spa mafia around here will be greatly appreciated.

Thank you for reporting this comment. Undo
repair_guy

Congratulations on your investment in the DDTC part. Will you be eating at McDonalds this month?

The ERR code is only one of two things. Improper voltage or a bad temp probe.

1. Chances are you did not change voltage lately but highly likely you forgot to reconnect the temp probe onto the board.

2. If you did connect it, the thing is bad. Is it a yellow cord or white? White are lousy and it is certainly shorted.

What was the symptom that caused the board replacement?

    Bookmark   November 30, 2007 at 4:15PM
Thank you for reporting this comment. Undo
bigredpepper

The original symptom was that there was no information on the DDTC except for a Pressure SW indicator. Replacement of the DDTC module fixed that.

What I have found since I posted is that I have only 13.7vac coming off the transformer, with good line voltage going in. It seems that these transformers are fairly standard, so I will be getting one tomorrow.

That might explain why my DDTC fried, right?

Seems it would be simple to have incorporated a low volt fault system to keep a 5.00 transformer from killing a 300.00 DDTC.

    Bookmark   November 30, 2007 at 6:00PM
Thank you for reporting this comment. Undo
repair_guy

The transformer better be the NT specific one (471571). Others will not work. Make sure you get a good solid ground on it or it won't fire.

You may have a short somewhere that fried your board and transformer.

    Bookmark   November 30, 2007 at 11:34PM
Thank you for reporting this comment. Undo
prestige_boy_yahoo_com

My four year old mini max heater just failed. It won't fire and only the power and pressure leds light up. I checked the sensors with a multimeter and all seem to be working. When I tap the black relay module on the DDTC board the blower comes on for about 5 to 10 seconds and then shuts off. Any ideas? Like you I hate to put out $300 for the board only to find out that it is something else!

    Bookmark   June 4, 2008 at 3:15PM
Thank you for reporting this comment. Undo
repair_guy

You need to see the lights on the back of the board.

    Bookmark   June 4, 2008 at 6:12PM
Thank you for reporting this comment. Undo
shanec

my heater reads off in pool or spa mode and persure switch light is off please help

    Bookmark   January 20, 2009 at 1:55PM
Thank you for reporting this comment. Undo
Rack Etear

It would be better if you started a new thread, but if it says "off" that means that the contacts on the pressure switch are open for one reason or another.

Common causes of this are.

1. Dirty filter.
2. Dirty stainer baskets
3. Clogged impeller
4. bad pressure switch.

There are many others, but these are the ones that I would start with.

    Bookmark   January 22, 2009 at 12:45AM
Sign Up to comment
More Discussions
My pebble sheen finish is so uneven...
Our pebble sheen finish was completed on January 1st...
Susan Scearce
Transition between two DiamondBrite colors
Trying to figure out best way to do this. Will be doing...
jscozz
Resurfacing a Pool
We are looking to resurface our pool. Can you give...
rhondasumsky
Atlantis pool and spa (Magnolia Tx) anyone have any feedback?
Searching for a pool builder and looks like Atlantis...
makingbeacon
Diamod Brite pool color photos
PLEASE!!!! Need to see finished pool pictures with...
Braden Taylor
Sponsored Products
Pentair Replacement Cartridge for S8M150 450 Sq. Ft. - NFS202S
$229.99 | Hayneedle
Pentair Replacement Cartridge for S7M120 300 Sq. Ft. - NFS200S
$199.99 | Hayneedle
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™