I'm planning to extend my deck across the back of my house. It will require me to fasten a ledger to the concrete foundation of the house. The foundation is poured reinforced concrete 8 inches thick, and is 3 years old. What is the best way for an amateur to attach the ledger to the foundation?

Thank you for reporting this comment. Undo
brickeyee

Rent a hammer drill and a 1/2 inch bit.
Drill holes that meet waht the AHJ wants for spacing.
Lead shell anchors and lag screws are not allowed in many places any more since they have poor withdrawal strength (the deck can pull the ledger away from the house and collapse).

Any of the expansion anchors on the page below are simple to install. The same size hole is used through the ledger into teh masonry. This eliminates trying to spot holes from the wood to the masonry.

Here is a link that might be useful: Rawl anchors

    Bookmark   August 13, 2006 at 2:31PM
Thank you for reporting this comment. Undo
john_hyatt

I use a rotary hammer,same 1/2'' bit, ss threaded rod and the two part hilti material,as a given it is high dollor stuff the two hole gun is around $60,they have a quick set and one thats a little slower but a person can build bridges with this stuff,it is impossible to get the rod out after this material has set up.Tap con the ledger to the wall just to hold it in place,drill thru the ledger into the wall,push the hilti into the hole it mixes as it runs thru the gun, twist the rod into it, use a big washer and double nuts. Bang Bang you are done forever. John

    Bookmark   August 13, 2006 at 6:59PM
Thank you for reporting this comment. Undo
java_man

Thanks for the info and links. I'll use expansion anchors.

    Bookmark   August 14, 2006 at 11:25AM
Thank you for reporting this comment. Undo
brooklyndecks

Java mon,

I use lots of galv. 1/2"x4" lag bolts into lag shields...expansion anchors. My decks aren't collapsing.

steve

    Bookmark   August 15, 2006 at 5:44AM
Thank you for reporting this comment. Undo
srercrcr

I used the same, only 5", and lots of em.

    Bookmark   August 15, 2006 at 7:37AM
Thank you for reporting this comment. Undo
brickeyee

"I use lots of galv. 1/2"x4" lag bolts into lag shields...expansion anchors. My decks aren't collapsing."

Not allowed by code uin many locations.
Lag screws and lead shields have very poor withdrawal reistence.
The decks can pull away from the houses and collapse.
They dio not move part way, but typically fail all at once when a large number of people are present loading the deck.

The link below is a typical set of deck requirements.
Lag screws for ledgers are only allowed for attachment to band joists. A lesson learned after hard experience.

Here is a link that might be useful: Deck Construciotn Guide

    Bookmark   August 15, 2006 at 10:10AM
Thank you for reporting this comment. Undo
brooklyndecks

yeah, I've read the fairfax county code already. I'm in Kings county, Brooklyn. I don't use lead shields. When I'm done bolting my ledgers into brick with two 1/2" bolts every 18", there is no way that the ledger is ever going anywhere. If I had any doubts, I wouldn't do it.

steve

    Bookmark   August 15, 2006 at 4:39PM
Thank you for reporting this comment. Undo
brickeyee

Then what are you claiming the "lag shields" are made from?
The harder material have even less strength then the softer ones, and the soft ones are a disaster.

    Bookmark   August 15, 2006 at 6:34PM
Thank you for reporting this comment. Undo
brickeyee

Just to give you an idea how bad lag shields are, a ½ in diameter long lag shield embedded 3 in deep into 2000 PSI concrete has a tension load rating of 2085 pounds. With normal derating it is allowed to hold 208 pounds.

A ½ inch Rawl Power Stud embedded 3 inches deep in 2000 PSI concrete has a tension load rating of 5100 pounds. With derating 510 pounds.

A 208 pound withdrawal every 18 inches on a deck is pitifully low and can easily be exceeded under normal conditions. As soon as the deck has any pitch the loads change from shear to tension.

Lag shields are not a safe method of attaching ledgers to concrete for deck support.

    Bookmark   August 15, 2006 at 6:47PM
Thank you for reporting this comment. Undo
srercrcr

Like Whoopi said..."Speak English, Mick!"
I assume tension load is the ability to not pull out.
Of course nobody has mentioned how much torque was applied to the bolt.
So now what is derating? I'm suspect of what youre gonna say cause both 200 and 500 lbs are not big numbers.
But I do appreciate you sharing.

    Bookmark   August 15, 2006 at 7:55PM
Thank you for reporting this comment. Undo
john_hyatt

Im telling you guys,go with the hilti system/ss threaded rod.Its a total done deal. J

    Bookmark   August 15, 2006 at 9:38PM
Thank you for reporting this comment. Undo
brickeyee

You build decks and do not even know what shear and tension loads in fasteners are????

"Of course nobody has mentioned how much torque was applied to the bolt. "

Cause it actually does not matter once you apply enough to obtain the maximum rating of the fastener. More torque can actually decrease the strength. If the shield starts to rotate in the hole the withdrawal resistance has been seriously compromised. It can turn at the start of tightening a little, but once it starts to expand it must stop rotating and not start again.

You have not provided adequate resistance to the fasteners pulling out of the wall (tension loading).
The numbers I used are for Rawl shield anchors at nominal installed strength.
Normal derating is to 10% of the ultimate strength so a 2000 pound strength is rated as only 200 pounds in actual use.
200 pounds if allowable tension load over 18 inches is only 133 pounds per foot of ledger. That is not a large number at all, and grossly inadequate.
500 pounds is 333 pounds per foot of ledger. Still a little low but could be acceptable if the deck is not very high off the ground (less than 4 feet or so) and not very large (say less than 8 feet perpendicular to the ledger).

Higher or larger the fastener spacing needs to be tightened up based on the actual area.

Positioning the anchors in a perfectly straight line in the wood also reduces the strength. The wood can simply split along the line of anchors and the deck pulls away.
The arrangement is normally for the anchors to alternate being 1/3 down from the top of the ledger, and the next one third up from the bottom.

As a PE I testify at trials over deck collapses.
Many times I just present the findings to the insurance company and they settle.
The Fairfax code is just one of many that have been promulgated over the past 10-15 years following deck collapses, many with serious injuries and even a few deaths.
A more recent problem has even been the overloading of band joists in frame houses and the entire side of the house (band joist, sheathing, etc.) all pulling away. Most of the nailing fastening the band joist is in tension (either through the joist into the ends of the floor joists, or through a joist hanger and into the band joist) and tension loaded nails have reduced strength. In the case of no joist hangers the nailing is into end grain and is normally rated at zero strength in withdrawal for structural purposes.

    Bookmark   August 15, 2006 at 9:51PM
Thank you for reporting this comment. Undo
srercrcr

Don't assume all the forum contributors build decks. They don't.
I understand shear and tension strength as it relates to the fasteners themselves. But when we're talking about the ability of the deck to pull away from the slab we're talking the combination of the bolt, shield, and concrete.

You didn't define "derating", you only applied percentages.
It sounds like youre saying a fastener system can only be counted on for 10% of it's maximum capacity. Is that so?

    Bookmark   August 16, 2006 at 7:13AM
Thank you for reporting this comment. Undo
brickeyee

The derating is the percentages of the optimal installation load.
Where human safety is involved and installation is not supervised by licensed engineers and actual testing performed to verify the installation, it is typical to allow loading of anchors to not exceed 10% of the ideal installation strength. For supervised installations the loading is normally ~12%, and for non-life type loads 25%.
You do not get a lot by doing the testing, so it is rarely performed. It is cheaper to just add enough fasteners to meet the 10% rating.
The derating makes up for the variation in installation (holes size, smoothness, variation in concrete, installation technique, etc) and the lack of any testing to ensure the actual installation.
In many cases even the strength of the concrete the anchors are installed in is not reliably known.
To be allowed for use the devices are required to be listed by a recognized testing authority and they must be installed with full compliance of the device instructions and any special conditions in the listing.
Listings typically list optimal load ratings for the anchors in various strengths of concrete. Other conditions to meet the listing are device spacing from edges and other fasteners and device depth.
Only a few people died before lag shields were disallowed and more secure fastening means required.
In the overall scheme of things the cost difference per job is very small and the gain in safety has been excellent. Deck collapses from ledger pull away have significantly decreased.
The most recent failures have been pulling away of entire band joists. There are probably going to be some additional changes in a few years if the problem persists.

I know many posters here are not deck builders, but at least one above is and appears proud he does not know what he is doing.
I hope he has good liability insurance.

    Bookmark   August 16, 2006 at 9:42PM
Thank you for reporting this comment. Undo
brooklyndecks

Brickeye,

I like to stay out of these debates, especially with know-it-all number crunchers...but you seem to want to drag me back in. You like to use terms like derating, and throw numbers and %s at us. you know what they say..."figures don't lie, but liars figure"

let's look at your data...you say those 1/2" bolts with 3/4"
shields will support 208 lbs (with derating). So if I use 2 every 18"...typically 20-30 per ledger...what will that support? what if I always fasten to brick, not concrete? those bolts are not gonna shear, so we're just talking about pulling away from the house. Add to that, a series of posts (4x4 or 4x6) supporting the deck about 8' out. those posts are set in concrete, at least 2.5' deep.

you're an engineer, and you testify at trials over deck collapses. how many trials have you been to where a deck collapsed because of lag shields? I'd like to read some supporting articles. Even if you can site a few examples, who knows who the contractor was, or who he hired to do the installation. Was it his first deck? was it a friday afternoon or monday morning? into brick? 1/2" bolts?

you can throw your numbers around, but you're not a deck builder...and you're certainly not on my site to witness the way I set a ledger.

Most decks collapse because the builder used nails to fasten a ledger into a rim joist. I've read articles about them. I never even deal with rim joists or nails. here in brownstone Brooklyn, my clients all have brick buildings. I've built plenty of parlor floor decks in the last 15 years, and I am confident that they will stay up at least until the wood deteriorates (nothing lasts forever).

Proud? yeah I'm proud of my work. check out my website if you want to see what I do. and don't worry about my liability insurance.

steve

    Bookmark   August 17, 2006 at 5:44AM
Thank you for reporting this comment. Undo
srercrcr

Thanks for the explanation Brick....

It's as I thought, I would state it as "being we don't know who built it, we're allowing for most things to go wrong."
And that's OK.
A factor I haven't heard mentioned was a deck that isn't level. You get a bunch of people on a deck that has a slope and that increases the tension tremendously (IMO).
On the other hand... a large, "overbuilt" deck weighs ALOT...in my calculations like 2000-3000 pounds. If the deck is level that's alot of weight going straight down. If good piers...no problemo. As a non-engineer, with enough mass and excellent piers there might even be a resistance to pulling away from the house, or in any direction. The height would have alot to do with it. Are you with me on that concept.

    Bookmark   August 17, 2006 at 7:01AM
Thank you for reporting this comment. Undo
irishbrewer

Not all anchors are created equally. The red-head wedge-type anchors work very well in concrete and are commonly used in construction/industrial applications.

Because the wedge grips the concrete more and more as you torque the nut, you do want to make sure you apply the proper torque during installation. Also, make sure you drill the proper diameter hole. I have included a link to the specs below and as you can see, even the little guys can develop quite a bit of strength (scroll down to the strength tables using the link) - much more than a couple hundred pounds quoted by brickeye.

Here is a link that might be useful: Red Head Wedge Anchors

    Bookmark   August 17, 2006 at 7:46AM
Thank you for reporting this comment. Undo
irishbrewer

Note: I should have said "...much more than a couple hundred pounds quoted by brickeyee for the lag shield anchors"

IMO, the lag shield type anchors are very much inferior to the wedge type shown in brickeyee's link and the alternate link I provided. These anchors can be purchased at a reasonable price at the big box stores and they work well so I don't see a good reason to use the lag shields.

    Bookmark   August 17, 2006 at 11:34AM
Thank you for reporting this comment. Undo
srercrcr

"Because the wedge grips the concrete more and more as you torque the nut, you do want to make sure you apply the proper torque during installation."
>>>> That's exactly what a lag shield does.

    Bookmark   August 17, 2006 at 3:52PM
Thank you for reporting this comment. Undo
brickeyee

"That's exactly what a lag shield does."

Lag shileds are all made from softer metals (lead or zinc being common) and do not have the strength of steel expansion anchors. Red head, Rawl exapansion anchors, they all work about the same.
The expanding steel will not slip the same way a shield type anchor does and the pressures that can be developed against the sides of the hole are nothing compared to steel anchors.
The guard rails on highways are attached using steel expansion anchors for a reason.
The strength and repeatability of steel anchors os far superior to soft metal anchors.

"If the deck is level that's alot of weight going straight down."

Decks are rarely level ebnough to eliminate tension loads, and are very unlikely to stay level for very long after construction. Wood moves.
Even the sagging of joists affects the loads on the anchors of the ledger.

    Bookmark   August 17, 2006 at 11:58PM
Thank you for reporting this comment. Undo
irishbrewer

Further to brickeyee's point about sagging and the load on the anchors:

"Even the sagging of joists affects the loads on the anchors of the ledger."

The sagging of the joists causes a rotation of the ledger board and due to the constraint of momvement caused by the concrete wall, the ledger board does not rotate about the anchor bolts but rather the lower edge of the ledger that is in contact with the concrete.

This results in a tensile load on the anchor bolts rather than just a shear loading. As such, the pullout performance of the anchor bolts is important.

    Bookmark   August 18, 2006 at 1:49PM
Thank you for reporting this comment. Undo
derekjoel_gmail_com

I looked at the Red Head anchor and not only do they support very good load #s, they also state the following:

"Allowable values are based upon a 4 to 1 safety factor. Divide by 4 for allowable load values."

That is vastly different from the 10-1 safety factor talked about earlier in this thread. Using the #s provided by The Smith Fastener Company website for shear and tension loads, you could fasten your ledger to your foundation so that even several full size pickup trucks yanking on it couldn't pull it out.

    Bookmark   March 28, 2009 at 11:27AM
Thank you for reporting this comment. Undo
Melm813_yahoo_com

Can someone in English please tell me hoe to atattch a ledger to concrete porch slab for the purpose of adding three foot staircase?

    Bookmark   August 15, 2011 at 1:42PM
Sign Up to comment
More Discussions
Venting a wood column to prevent rot
I have purchased some old wood columns that are stave...
dustynight
Ipe vs. Thermory
First post of what I anticipate may be many as we embark...
lmgch
Ideas for front porch needed
Hello. We bought a house that was new construction....
jsandlin0803
azek harvest/terra? timbertech xlm? trex escape & transcend? help
I am at my WITS END going crazy trying to sort through...
tyjy
Best concrete sealer to prevent salt damage? Any virgin concrete
I'm not sure which part of the forum this question...
growingadvice
© 2015 Houzz Inc. Houzz® The new way to design your home™