Help calculating beam load

onikoroshiMarch 8, 2012

Hi,

I have an existing enclosed patio and would like to turn the roof into a deck/balcony.

The patio is 14'x22' with a 6x14 beam held up by 6x6 posts 14' away from the house. The beam is running parallel with the house with 2x10 joists supported by the house itself and the beam.

Assume the live load and dead load on the building's roof is 50 PSF, may be 60 PSF (I live in California but I need to double check this).

The weight bearing on the beam should be: 14*22*50/2 = 7,700 pounds, since the beam only holds half the roof's weight.

Assume allowable fiberstress of beam is 8.

Maximum bending moment: Mmax = WL/8

Mmax = 7700 * 22 / 8 = 21,175 ft/lbs

(Should this length be 14 ft not 22 ft?)

Section Required = Mmax X 12 / Fb

21175 ft/lbs * 12 in/ft / 1000 PSI = 254.1 cu in

Section modulus of my beam is: S = bd2 / 6

S = 6 * (14*14) / 6 = 168 cu in

Either my math is wrong or this big, beefy 6x14 beam isn't nearly as strong as I would suspect.

Deflection and sheering are more than adequate with the 2x10 joists.

b = 1.5

d = 9.25

Deflection: D =(5 * W * L3) / (384 * E * (b * d3/ 12))

Shear =(( 3 / 2 )* V ) / ( bf * df )

Thanks in advance.

Thank you for reporting this comment. Undo
PRO
Sophie Wheeler

Just call a structural engineer. You will need one to stamp any plans you present to the permit department.

    Bookmark   March 8, 2012 at 8:14PM
Sign Up to comment
More Discussions
Help finishing inside screened porch
Need suggestions. I don't know how to finish the top...
hlastala
Travertine medallion on porch
Hello We had water stained our concrete porch but the...
Rigbyblue
Venting a wood column to prevent rot
I have purchased some old wood columns that are stave...
dustynight
clear roof over patio
I would like some advice/help with the clear roof over...
ktmast
deck Shade Tree canopies
Does anyone have these? How much do they cost (ballpark)?...
caflowerluver
© 2015 Houzz Inc. Houzz® The new way to design your home™