Lift Station Basement-Air Bubbles BR Above

heidi_tapleyNovember 21, 2012

We have a Liberty sewer pump system installed in our basement bathroom, and it has been in use for about 8 years. We haven't had any problems until recently. Now, when the lift station turns on and begins pumping, it causes problems in the bathroom on the main level of the house which is directly above the bathroom. I get large air bubbles in my toilet and can hear gurgling in the shower drain. What would cause this?

Thanks!

Thank you for reporting this comment. Undo
brickeyee

Incorrect venting.

Pump pits require there own dedicated vent line not shared with anything else but run directly to free air.

    Bookmark   November 21, 2012 at 7:48PM
Thank you for reporting this comment. Undo
heidi_tapley

It has its own dedicated venting and no obvious clogs since everything drains quickly -that is what has us puzzled.

    Bookmark   November 21, 2012 at 8:55PM
Thank you for reporting this comment. Undo
brickeyee

You have described something simply not possible.

The venting is shared at some point, or the pump is generating a whole lot of back presre in the drain and is not vented correctly.

If the venting was correct there could be no way to make a bubble come from a toilet with an ejection pump.

    Bookmark   November 22, 2012 at 2:06PM
Thank you for reporting this comment. Undo
heidi_tapley

The Liberty pump station has it's own dedicated vent up from the buried tank and the main level bath vents out into attic area. The pump station and main level bathroom do share a drain line to the septic tank, with the main level bath being closer to the septic tank.

    Bookmark   November 22, 2012 at 3:44PM
Thank you for reporting this comment. Undo
kirkhall

When was the last time your septic tank was pumped?

    Bookmark   November 22, 2012 at 8:11PM
Thank you for reporting this comment. Undo
lazypup

Where and how is the lift station connected to the house DWV system?

    Bookmark   November 23, 2012 at 1:40AM
Thank you for reporting this comment. Undo
heidi_tapley

Thanks. Didn't even think about septic being full. I am not aware that it has been pumped in the 9 years I have lived here.

    Bookmark   November 23, 2012 at 12:00PM
Thank you for reporting this comment. Undo
kirkhall

On septic pumping timeframes:

Here is a link that might be useful: GW post about pumping septic systems

    Bookmark   November 23, 2012 at 1:23PM
Thank you for reporting this comment. Undo
lazypup

A septic tank is always full and pumping the septic tank will have nothing to do with the problem at hand.

    Bookmark   November 23, 2012 at 2:58PM
Thank you for reporting this comment. Undo
kirkhall

I just know that when my parents had trouble with sewage backing up--it was because the septic needed servicing. My thought was that if the "troubled" drains are closer to the septic tank than the other, perhaps the tank is nearing a service time.

If it hasn't been serviced in over 9 years, it is probably time to do so, regardless of whether it solves your problem or not (and if it solves the problem, BONUS!)

(Report back?)

    Bookmark   November 23, 2012 at 11:20PM
Thank you for reporting this comment. Undo
heidi_tapley

Back for more help.

Son went away to college so downstairs bath wasn't being used. Now that he is back the bubbling has continued.

Since this posting we had septic pumped, check valve replaced and lower level venting checked.

I have noticed before I hear the ejector pump kick in to push water out, the water in the upstairs toilet slowly drains down and then there is a gush of bubble coming out as pump kicks in to push water out. There are two AAV vents in the attic. One is for the main bath area, and the another on the other side of the house above kitchen, laundry room. In the crawl space area where ejector pump is the pump has a separate vent pipe coming straight up and the vanity, toilet and shower are connected to and AAV vent.

Any other suggestions?

    Bookmark   June 8, 2013 at 6:06PM
Thank you for reporting this comment. Undo
brickeyee

"I have noticed before I hear the ejector pump kick in to push water out, the water in the upstairs toilet slowly drains down and then there is a gush of bubble coming out as pump kicks in to push water out."

It still sounds like the vents for the pit and the rest of the system have become interconnected.

They are required to remain separate, all the way to separate holes in the roof.

The pits vent line must run all by itself all the way to free air.

    Bookmark   June 9, 2013 at 11:35AM
Sign Up to comment
More Discussions
Terminox ISM for iron/manganese removal
Hi, I have had a water softener with other assorted...
merlin2552
Water Softener - Help with Proper System Selection
Hello, I decided to put in a water softener system...
badsha
Hot water backflowing into cold supply
OK, I'm rephrasing my question, as what I'd asked before...
pjb999
Fed up and ready to tackle my well water issues
I've been reading posts trying to educate myself for...
nutherokie
Costco Water Ridge Dual Flush -- Need reviews
Any more reviews on the dual flush Water Ridge toilet?...
smudgecat99
Sponsored Products
Large Quilted Jewelry Box
$199.00 | FRONTGATE
Spectrum Blue Rectangular Throw Pillow with Sunbrella Fabric, Set of 2
$49.99 | Bellacor
KOHLER Bathtubs Mariposa 6 ft. Right Drain Bathtub in White K-1257-VBRAW-0
Home Depot
Hoppi Chrome One-Light Halogen Square Canopy Wall Sconce with Marble Glass
$162.00 | Bellacor
Copley Swivel Chair - Key Largo Grass Green
Joybird Furniture
Glass Lemonade Beverage Dispenser on Rattan Base
Classic Hostess
Kraus C-GV-103FR-12mm-10 Frosted Brown Glass Vessel Sink and Waterfall Faucet -
$239.95 | Hayneedle
Nourison Indoor/Outdoor Nourison Rugs Escalade Denim 2 ft. 3 in. x 8 ft. Runner
Home Depot
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™