What is the best way to vent a wall mount toilet? I am using a Grohe in wall carrier. The horizontal line will be about 12 inches below the floor level. It is a single story. From what I can tell I have 2 options. Is either option preferred or is there another option I don't see? Thank you.

1) Outlet pipe goes straight down to the main horizontal drain line under the floor and have the vent come off the horizontal pipe just upstream of the toilet connection.

2) Have the outlet pipe go at an angle and connect to a vertical pipe that connects to the horizontal line and goes up though the roof as the vent line.

Thank you for reporting this comment. Undo
davidro1

3) Direct the outlet pipe sideways (not angled down) to a Tee. The Tee is vertical. This is where the outlet goes downwards. The vertical pipe (top end of the Tee) goes up though the roof as the vent line.

Hope this answers your first question, "... best way to vent..."

    Bookmark   November 19, 2010 at 11:12AM
Thank you for reporting this comment. Undo
brickeyee

"The Tee is vertical. This is where the outlet goes downwards."

Use the correct type of T.

    Bookmark   November 19, 2010 at 12:24PM
Thank you for reporting this comment. Undo
kaffine

From the instructions that came with the wall carrier the outlet pipe can not go horizantol. It is either staight down or +- 45 degrees from straight down. So do I ignore those instructions and vent the way Davidro1 said?

    Bookmark   November 19, 2010 at 4:44PM
Thank you for reporting this comment. Undo
lazypup

Drop it straight down.

If your under the UPC you can then place a vertical vent anywhere within 8' on the horizontal run.

If your under the IRC it don't need a vent.

    Bookmark   November 19, 2010 at 5:42PM
Thank you for reporting this comment. Undo
davidro1

Have you called the Grohe technical support number?

The "+- 45 degrees from straight down" is the preferable of the two you wrote in your first post. To answer your question "... best way to vent..."

Your Q "... best way to vent..." is one question. But, you don't need venting as early in the line as I wrote it, or as you wrote it, since toilets are designed to work without being vented. Also.

Post a link to the web PDF that has the Grohe carrier. Then, further discussion can happen in this thread.

I have a Geberit carrier and the pipe can be swiveled sideways.

    Bookmark   November 19, 2010 at 9:48PM
Thank you for reporting this comment. Undo
manhattan42

Lazypup gave the correct answer.

Venting for water closets is determined by your local plumbing code.

    Bookmark   November 20, 2010 at 11:24PM
Thank you for reporting this comment. Undo
kaffine

Thank you for the replies.

I am under the UPC so I will have to vent it.

I read the manual again and I could have sworn it said it could only go 45 degrees from straight down but I don't see it now. It only mentions the drain pipe going straight down. The manual isn't all that great though.

I am overly concerned about the venting because the last owner did a lot of plumbing work with no permit and apparently no vents. So I am having to redo a lot more than I wanted so it will be correct and work.

Here is a link that might be useful: Grohe manual

    Bookmark   November 23, 2010 at 2:25AM
Thank you for reporting this comment. Undo
lazypup

The 45 deg angle is a critical angle because in plumbing any line that runs horizontal or rises at an angle up to 45deg above horizontal is technically defined as a "Horizontal Line"

Any line which rises at any angle from 45deg above horizontal to straight up at 90deg above horizontal is technically defined as a "Vertical Line".

In essence what your instructions are saying is that the unit MUST BE attached to a Vertical Line.

Obviously that vertical line from your wall mount fixture will drop down and connect to a horizontal line at some point below the fixture.

Per code the line is a 3" line and under the UPC a 3" line may run a maximum of 8' horizontal from the trap weir to the vent opening.

Under the IRC a 3" horizontal line may run a maximum of 12' from the trap weir to the vent opening, however, there is an exception in the IRC that says if a water closet is the only fixture being served by the 3" horizontal line it may run an indefinite length.

To understand the reasoning here we must consider the reason why they have established maximum lengths from trap weir to vent openings.

For most fixtures the maximum limit from trap weir to vent is to insure adequate venting of the trap to prevent the trap from being siphoned out, thereby leaving the trap dry.

A water closet is the exception that proves the rule. By its basic design a water closet relies upon the siphon effect to lift the effluent up and over the trapway in the base of WC. This also explains why all water closet fill valves are equipped with a "Trap Primer" line to insure that the trap will be adequately refilled during the flush process.

In actual operation a water closet will have a better flush if the length of the water closet waste arm is maximized to the limits allowed by your local code.

    Bookmark   November 23, 2010 at 7:17AM
Sign Up to comment
More Discussions
shower neck leaking
Just installed a shower head (in new construction),...
sid_79
Rainfresh water filter leaks from top.
I have a Rainfresh water filter. It seems to be leaking...
gtrshop
Yes or No to Easy Water (no-salt) water softener?
I started this thread to reply to Sam because the prior...
peoplelover
Septic tank and question on the "Sponge"
I have a septic tank that when last pumped out had...
big_al_41
Pulldown sprayer leaking
My Moen pulldown faucet (with Reflex Technology!) was...
ginny20
© 2015 Houzz Inc. Houzz® The new way to design your home™