Relocating Toilet

joan2121August 19, 2010

I am relocating a toilet and need to put 3 1/2" holes in two floor joists to accomplish the move. The joists are 2" by 9" that are 12" on center. Is that a structural issue? Thanks.

Thank you for reporting this comment. Undo
peterfrost

Hi... I'm not an engineer... but if you are under the California code (CBC) which is basiically the 2006 IBC, solid sawn joists can be bored (a hole cut) to one third their depth (in your case a 3" hole in a 9.25" joist) in the outer 1/3 of the joist with a 2" minimum clearance from the edges (top and bottom).

Therfore, your situation (at 3.5") would not be compliant with the above code.

However, your question was, is that a structural issue... not is it within code. I don't have enough detail to know... and if it seems like it might be... you might have to consult an engineer with the full set of detail.

(In general circumstances, I would bet that it will not be a material structural issue... but I can not be certain.)

Good luck... Peter

    Bookmark   August 20, 2010 at 2:03AM
Thank you for reporting this comment. Undo
joan2121

Thanks for the input. I laminated 3/4 inch plywood on either side of the joist and drilled the hole. Second floor is still standing :)

    Bookmark   September 4, 2010 at 6:15PM
Sign Up to comment
More Discussions
Water Softener - Where to start?
I am looking to purchase a water softener given our...
sagosto
LaToscana Novello Thermostatic Shower Valve
Trouble with LaToscana Novello Shower Valve- no hot...
bathroomblues1
Fire Sprinkler
Purchasing a home with an indoor fire sprinkler system....
jglo
New under mount sink - drain off-center?
I had a new granite countertop installed with an under...
mike_lee2
Does reverse osmosis water corrode copper plumbing? The answer ..
The answer is YES. I did a very unscientific study...
ohmmm_gw
© 2015 Houzz Inc. Houzz® The new way to design your home™