TALDEMay 11, 2013

Hello.

Does anyone see any drain or venting issues with this rough in for a double sink ?? (All 1.5 inch pvc). The vertical vent tees into the shower vent in the attic and exits through the existing roof vent. I will be putting a 2x3 wall there, btw. Thanks!

Tom

Thank you for reporting this comment. Undo
SlugTheGardner

I believe the total length of 1.5 inch vent can be 25 feet total. I could not determine from your picture how you attached/supported the pipe.It's good practice to include pipe supports close to tees. It wouldn't hurt to put in a support at your short horizontal vent pipe, but I tend to overbuild. Make sure that the horizontal pipe is sloped 1/4 inch per foot.

See Section 905 of 2012 International Plumbing Code for venting connections. With your T into shower vent: vent connections must be at least 6 inches above the fixture/flood level being vented.

    Bookmark   May 15, 2013 at 9:26PM