Replacing Unvented Drum Trap with P-Trap and AAV

ntl1991April 15, 2012

Hello, I'm in the planning process of removing my Tub's Drum Trap and replacing it with a proper P-Trap and an Air Admittance Valve.

The tub is plumbed as follows in PVC:

1-1/2" Trap Adapter, Drum Trap with Cleanout, 4 feet of 1-1/2" PVC (slope = 1/2" per ft), 90 degree elbow to go vertical, 1' of 1-1/2" pipe, tee from lavitory drain, 5' 1-1/2" pipe into a 3" sanitary tee at the main drain.

The closest place to put the vent line would be right after the P-trap, with a wye, going backwards at an angle, and up into the wall cavity behind the tub, which is accessable from a closet.

I could also put the vent at the top of the vertical drain from the tub, but I don't have much space to get me the 4" distance from the trap to the AAV. I'd have to drop the P-trap a few inches, or increase the slope of the 4' trap arm.

I made a little picture to explain my current setup and options. Which way can I go?

Thanks,

Nick

Thank you for reporting this comment. Undo
Ozone89

How far away is the tub from the main drain? If you're within 6' you don't need a AAV unless you have 2 fixtures behind a vent. The best way to explain that to you is...if you fill up the tub and drain it, does the sink or toilet in that room make a sucking sound?

By code, AAV's or back vents are supposed to terminate 6" above the highest fixtures flood rim on that line.

    Bookmark   April 16, 2012 at 12:32AM
Thank you for reporting this comment. Undo
lazypup

Under the IPC & IRC the maximum length of a fixture arm can be computed by dividing the diameter of the drain by the pitch. If an 1-1/2" line is installed with the code standard 1/4" per foot pitch the maximum lenght would be 1.5 / .25 = 6ft but in this instance the line has a 1/2" pitch so the maximum allowable length would be 1.5 / .5 = 3'. (The bottom of the drain line at the trap weir may not be higher than the top of the line at the vent opening).

Both the configurations illustrated above would not pass code for a number of reasons.

The simple solution would be to remove the drum trap & extend the length of the tub drain tailpiece. Code will allow up to 24" vertical drop from the tub drain opening to the water level in the trap.

Attach a P-trap and run the line with a 1/4" per foot pitch.

A wye can be installed on the drain line with the side input angling downstream. You can then put a street 1/8bend on the wye side opening input, which would turn the side opening vertical and attach an AAV where the base of the AAV is 4" above the drain line.

REF-IPC
917.4 Location. The air admittance valve shall be located a
minimum of 4 inches (102 mm) above the horizontal branch
drain or fixture drain being vented The air admittance valve shall be located within the maximum developed length permitted for the vent. The air admittance valve shall be installed a minimum of 6 inches (152 mm) above insulation materials.

    Bookmark   April 17, 2012 at 7:46AM
Sign Up to comment
More Discussions
Doable...European sink & US bathroom pop-up drain and faucet?
if I purchase a small Belfast sink fron England to...
rantontoo
Water softener decision for Austin, Texas city water
I want to better protect my plumbing from wear and...
ivaniphone
Marble shower panels valve replacement :( !!!
We have a couple of bathrooms with a single handle...
Vamsi Kodavanty
Terminox ISM for iron/manganese removal
Hi, I have had a water softener with other assorted...
merlin2552
Help, water filter?
I recently bought a rural home, and have yet to move...
dmnwlkr
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™