Horizontal Vents 6 inches above tallest fixture

spafrica2003April 28, 2010

I have been told that "code prohibits any horizontal vents until the vent reaches an elevation 6" higher than the tallest fixture served by that vent."

If I want to run a 2" vent off of the 4" stack/vent, do I have to enter 6" above the highest fixture itself or 6" above the highest point on the stack where a drain line enters the stack?

Thank you for reporting this comment. Undo
brickeyee

6" above the highest fixture itself

It is to make sure the vent stays dry and does not have waste in the line.

    Bookmark   April 28, 2010 at 4:46PM
Thank you for reporting this comment. Undo
lazypup

A vent line may not run horizontal until it reaches an elevation at least 6" above the highest fixture served by that vent.

The same rule applies to a stack. You may not attach a vent line to a stack until you reach an elevation at least 6" above the flood level rim of the highest fixture served by that stack.

By example, if you are venting a bathroom on the first floor and you need an auxiliary vent, the horizontal offset of that auxiliary vent would need to be at least 6" higher than the lavatory bowl rim in that bathroom. If you want t6o attach that vent to the stack serving both the first and second floor you cannot attach the auxiliary vent to the stack until it reaches a point on the second floor which is 6" higher than the flood level rim of the highest fixture served by that stack on the second floor.

Also, Under the UPC vents are sized by the dfu's load of the fixtures served by that vent, but if there is a horizontal offset longer than 3" the entire length of the vent must be increased one nominal trade size.

    Bookmark   April 28, 2010 at 5:43PM
Sign Up to comment
More Discussions
Cold Water TOO COLD! What to do?
I know there is a lot of concern over regulating hot...
mrb6228
troubleshooting thermostatic valve for shower
troubleshooting thermostatic valve, no hot water and...
bathroomblues1
Septic tank and question on the "Sponge"
I have a septic tank that when last pumped out had...
big_al_41
Does reverse osmosis water corrode copper plumbing? The answer ..
The answer is YES. I did a very unscientific study...
ohmmm_gw
Water pressue and other plumbing issues (MULTIPLE ISSUES - LONG)
I have a couple plumbing issues in my house. Some background... Approximately...
gtrshop
© 2015 Houzz Inc. Houzz® The new way to design your home™