jchangApril 14, 2009

I recently measured the water pressure at my house after one of my water heaters release valves dumped a bunch of water on my basement floor. It looks like the water pressure is arouind 80-85 PSI with a peak of 95 PSI. This seemed a bit high, so I called my water company and they said that my neighborhood pressure is set at 85PSI and this was an optimum level, especially for water heaters.

Does that sound right? Should I look into installing a pressure relief valve in the house?

Thanks for any insight.

Thank you for reporting this comment. Undo
lazypup

Code Maximum is 80psi.

In any instance where the pressure exceeds 85psi, even intermittently we are required to install a PRV (Pressure Reducing Valve) and an "Expansion Tank" in the near proximity of the water heater.

REF:
Uniform Plumbing Code UPC-608.2
International Residential Code IRC-2903.3.3.1

    Bookmark   April 14, 2009 at 11:36AM
Thank you for reporting this comment. Undo
jchang

Thanks - it did seem high. Is it unusual for the water company pressure to be so high (and even more so for them to say that 85 PSI is "optimum")? I think I will go ahead and do both the PRV and the expansion tank.

    Bookmark   April 14, 2009 at 1:27PM
Thank you for reporting this comment. Undo
pjb999

It's a good idea. There is no guarantee that the pressure won't exceed 85, and it will shorten the life of the wh and other parts, and increases the risk of an unexpected flood.

If at times of high demand your supplied water pressure drops, your prv will not 'boost' it, it will only bring pressure down to spec. You won't notice any adverse effect otherwise.

An in-line pressure gauge permanently connected ( a decent stainless steel-bodied one) wouldn't be a bad idea, you will want some sort of pressure gauge on hand when you're setting up the expansion tank as you have to 'equalise' the pressure within the tank bladder, if you're doing it yourself.

    Bookmark   April 14, 2009 at 4:42PM
Thank you for reporting this comment. Undo
lazypup

In a municipal water supply system the static head pressure on the system is primarily generated by means of water towers.

Water exerts 0.434psi per/ft on a vertical column of liquid. (Vertical Static Head)

In order to insure that the system will maintain the required code minimum of 45psi the support tower is 105' tall above average terrain to the base of the storage tank. (105' x 0,434psi= 45.57psi)

The storage tank on the top of the tower may then be as much as 92ft higher. (0.434psi x 92' = 39.92psi)

From this we can easily see that when the storage tank is empty we still have a static head pressure of 45psi, however when the tank is full the static head pressure at the ground level would be 45psi + 40psi = 85psi.

The storage tank is then fitted with a pump controlled by a float system very similar to the fill valve in a toilet tank. Wherever practical the system is allowed to use the water from the tank during the day and the pumps are set up to refill the tank at night when the electrical supply for the pumps is on an off peak demand.

Generally a municipal water supply will provide the highest static head pressure to your house early in the morning when the tank is full, but that pressure may decrease throughout the day as the water level in the storage tank drops.

To this point we have discussed the pressure above average terrain however the actual pressure at your faucet is a net result of the physical differential between the elevation of your faucet and the top surface of the water in the storage tank.

If your house is substantially above the average terrain elevation at the storage tank your water pressure will be less than the average for the community, and conversely, if your house is below average terrain your water pressure will be higher. By example, I am familiar with one community in W.PA where the town is built on steep hills. While the municipal water system can provide water pressures within the prescribed code range of 45-80psi for the majority of the community, there are neighborhoods at the bottom of the hills where all structures must be fitted with PRV's. On the other hand, some of the structures on the top of the hills actually require boost pumps to maintain code minimum.

As you can see from this, during the course of a day the line pressure could vary by as much as 40psi, depending upon the actual level of the water in the municipal storage tank. For this reason we do not install pressure gauges on systems supplied by a municipal water supplier because the gauge would not provide any truly useful information, and it would only cause undue apprehension of the part of the untrained homeowner, which would then results in hundreds of unwarranted complaints to the water supplier.

    Bookmark   April 14, 2009 at 9:42PM
Thank you for reporting this comment. Undo
asolo

Listen to lazypup on this topic....very helpful to me some months ago when my PRV failed and my house was subjected to 120-130psi street-pressure -- which is, in fact, intended nominal street-pressure for my neighborhood. My over-pressure problems/damages were over 6,000 before I woke up. Main evidence was my WH blowing out when I wasn't there. Painful.

    Bookmark   April 14, 2009 at 10:03PM
Sign Up to comment
More Discussions
Trying to verify gas pipe size
I am installing a new natural gas range and oven, and...
hoolabob
Hard Water or What?
We are renting an older duplex home in CT, and the...
roysterfam
Rainfresh water filter leaks from top.
I have a Rainfresh water filter. It seems to be leaking...
gtrshop
Inspection Hell (or why not to DIY)
Hi everyone, First time poster but long time lurker....
giantsean
troubleshooting thermostatic valve for shower
troubleshooting thermostatic valve, no hot water and...
bathroomblues1
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™