Advice on Carrier and Luxaire Quotes

engine15December 15, 2011

Hello, we live in a 1500 sq. ft. house in New Jersey. My HVAC system is about 25 years old, so I am looking to replace it and take advantage of some of the state rebates. I received a few quotes, and narrowed it down to these two:

Quote 1 - Luxaire System:

Furnace: TG9S080B12MP11, 95.5%, 80,000 BTU

A/C: TCJD36S41S1 3 Ton, 13 SEER

Coil: ???

Quote 2 - Carrier System:

Furnace: 59SP5A080E17-16 96.5% 80,000 BTU

A/C: 59SP5A080E17-16 3 Ton, 16 SEER

Coil: CNPVP4821

How do these two quotes compare? I'm leaning towards the Carrier system due to the price, but can't find much information on the A/C unit they are quoting. Any feedback would be appreciated.

Thank you for reporting this comment. Undo
mike_home

You have posted the furnace model number for the Carrier AC condenser. Can you correct it?

    Bookmark   December 15, 2011 at 8:47PM
Thank you for reporting this comment. Undo
engine15

The correct part number for the Carrier AC is CA16NA036.

    Bookmark   December 15, 2011 at 10:14PM
Thank you for reporting this comment. Undo
tigerdunes

Engine

You should recheck the Carrier AC condenser mdl number. Don't believe that's correct.

Have you asked for a load calculation? My first observation is that you are being oversized both heating and cooling.

IMO

    Bookmark   December 16, 2011 at 7:18AM
Thank you for reporting this comment. Undo
engine15

I apologize for the incorrect part number, here are the corrected numbers:

Quote 1 - Luxaire System:
Furnace: TG9S080B12MP11, 95.5%, 80,000 BTU
A/C: TCJD36S41S1 3 Ton, 13 SEER
Coil: ??? (still waiting to hear back from contractor)

Quote 2 - Carrier System:
Furnace: 59SP5A080E17-16 96.5% 80,000 BTU
A/C: CA16NA036 3 Ton, 16 SEER
Coil: CNPVP4821

The numbers I got from the contractor doing the manual J were 32379 Btuh for heating and 22921 Btuh for cooling. However, all my ducts run through a vented crawlspace, and I was advised not to insulate them due to the possibilty of the water pipes freezing down there. Would this impact the sizing?

    Bookmark   December 16, 2011 at 10:03AM
Thank you for reporting this comment. Undo
heatseeker

Luxair- run rabbit run go with carrier.

    Bookmark   December 16, 2011 at 10:15AM
Thank you for reporting this comment. Undo
tigerdunes

engine

I don't understand dealer's sizing versus the load calc.

And to be clear, your ductwork in attic is not insulated?

And dealer is comfortable and will stand behind installing a 95%+ condensing furnace in an attic install for a NJ location?

You need some other opinions on the above.

IMO

    Bookmark   December 16, 2011 at 10:24AM
Thank you for reporting this comment. Undo
engine15

tigerdunes,
The dealer that did the load calc suggested a 60k btu if I went with the Infinity system, but 80k btu for the Performance series.

I have a downflow system, the return in the attic is insulated, but the ducts that run through the crawlspace feeding the registers are not. The furnace is located in a first floor utility room.

    Bookmark   December 16, 2011 at 10:52AM
Thank you for reporting this comment. Undo
tigerdunes

Engine

And where does dealer plan on installing new furnace?

The furnaces quoted are both 95% eff condensing furnaces, Luxaire and Carrier.

And you still have not posted the correct Carrier AC condenser?

The supply lines should be insulated. Any reason why they aren't?

Post back.

IMO

    Bookmark   December 16, 2011 at 11:10AM
Thank you for reporting this comment. Undo
engine15

The new furnace would be located in the utility room as well, which is part of the house that is heated and cooled.

The AC Condenser is CA16NA03600G. I called the dealer, they said this is similar to the 24ABC6 series?

Not sure why the lines arent insulated, it looks like it was designed to use the losses from the ducts to prevent freezing. Could I insulate both the pipes and ducting in the space?

    Bookmark   December 16, 2011 at 12:25PM
Thank you for reporting this comment. Undo
mike_home

"The dealer that did the load calc suggested a 60k btu if I went with the Infinity system, but 80k btu for the Performance series."

This statement makes no sense to me. An 80K furnace is oversized reqardless of the number of stages or whether it is variable speed or not. Even a 60K at 95% AFUE is oversized. I don't get a good feeling about this contractor.

The CA16NA036 condenser and 24ABC6 series are builder's grade models. I recommend you spend the money to upgrade to a better model.

I assume the crawl space under the house is fully enclosed and insulated. How cold does it get in the crawl space in the winter?

    Bookmark   December 16, 2011 at 12:53PM
Thank you for reporting this comment. Undo
engine15

It didn't make sense to me either, unless it was done to get a rebate. Haven't called them about it yet, I plan on doing so sometime next week.

The crawl space is vented and open to the outside air, so it does get cold down there. I actually just recently added more insulation due to cold floors in some rooms. I've only lived in it for a couple of months now, so I'm still learning - should these vents be closed in the winter, or would it lead to moisture problems?

    Bookmark   December 16, 2011 at 1:40PM
Thank you for reporting this comment. Undo
mike_home

It is bad practice to oversize equipment in order to qualify for a rebate.

I would think you would not have to vent the crawl space in the winter. Does the area feel damp?

    Bookmark   December 16, 2011 at 8:24PM
Thank you for reporting this comment. Undo
engine15

The area doesn't feel damp, and there is a vapor barrier covering the entire floor. I guess I will just cover the vents for the winter and re-open them when it gets warmer.

    Bookmark   December 17, 2011 at 4:58PM
Thank you for reporting this comment. Undo
PRO
CJ Mechanical of North jersey llc.

The job of th hvac guy is to install the most efficient system possible. code requires duct to be insualted in unconditioned soace.have pipes insulated to protect from freezing and or dump a supply in the crwal.to suggest not to insulate??I would be concerned, insulate the crawl space ceiling.I install 90+ furnaces in attic all the time, over 20 yrs in north jersey.Need to know how to do it properly.

    Bookmark   December 17, 2011 at 10:34PM
Sign Up to comment
More Discussions
Thoughts on proposed HVAC system?
To start: my house is two-level (main plus upper)...
gbleeker
gas wont come on. forced air gas fired furnance
the Furnace was starting then running a couple minutes...
waterguytexas
Heat Pump.....will it really save me money?
I recently moves into a new house in Mass, a 1650 sq...
Jinx_1832
Replacing heat pump and keeping current air handler....
Well the good news is we are being blessed with a new...
piratechick
Geothermal (GSHP) replacement
My almost 80-year-old mother's house was built in 1998...
DavidR
Sponsored Products
Superman Pop-Up Bottle - Set of Two
$9.99 | zulily
Pet Life Airline Approved Folding Casual Pet Carrier - B5PDLG
$36.28 | Hayneedle
My Little Pony 'Friendship' Collapsible 12-Oz. Water Bottle
$6.99 | zulily
Kidwise Commercial Jungle Combo Bounce House - KE-CO2203
Hayneedle
Napa East Wine Barrel Lettered Staves - Carpe Vinum Multicolor - 1023-CARPE
$69.90 | Hayneedle
Barbie All Doll'd Up Lunch Box