What Should Furnace Supply Air Temperature Be

jaysgardenDecember 19, 2011

Two floor house with an unfinished basement.

Have a Goodman-single stage - natural gas - forced air - 100K BTU furnace. Last year I foil taped all joints in basement trunk line and 6" branches. Also used some mastic.

Main trunk line in basement runs perpendiclar to joists then take offs run in between basement joist cavities then booted up thru subfloor to supply 1st floor vents.

2nd floor vents are supplied by duct runs from basement up thru 1st floor wall cavities. Pretty standard installation I believe?

I only mention this to indicate there are no duct runs in a crawlspace or cold attic.

Now for question:

At the supply register approximately what should the temperature of the supply air be?

Thank you for reporting this comment. Undo
veesubotee

No way to answer that question as each specific furnace has a specification for outlet temperature and temperature rise.

The TR will be dependent upon how the furnace was set up (blower speed) and other factors.

All registers (runs) are not created equally. Depending on the design of the duct system, and the length of the trunks and runs, there will be differences in airflow through each. The longer the run, the slower the airflow, the greater the loss of heat will be along the run.

At a minimum, if you post the full model number of your furnace, someone can give you the specs mentioned above. Any information on blower speed will be helpful.

V

    Bookmark   December 19, 2011 at 1:56PM
Thank you for reporting this comment. Undo
jaysgarden

Goodman model GMPN100-4. Think I need to do my readings after furnace has been burning for at least 10 minutes.

    Bookmark   December 19, 2011 at 3:43PM
Thank you for reporting this comment. Undo
veesubotee

The temperature rise for your furnace is listed as 40 - 70*F. This is the difference in temp of the return air immediately before entering the furnace and the supply air, a few feet downstream of the furnace (out of sight of the HX), after a/c coil or in duct.

If you feel that the air coming out of the registers is cooler than with a previous furnace, it is likely due to the fact that it needs to blow more air to reach the higher AFUE value.

The installation guide (http://igate.northernplumbing.com/specsheets/goodman/gmpn.pdf) does not list a maximum outlet temperature. Try the furnace data plate.

Again, the temperature of air leaving the registers is subject to variation, as I indicated previously.

V

The

    Bookmark   December 19, 2011 at 4:51PM
Thank you for reporting this comment. Undo
jaysgarden

Thanks....I was going to ask where to take input air temp readings and output temp air readings to check the rise but you answered that above.

I take it if I have to drill a small hole in duct just downstream of A/C coil that is not a problem just cover it with foil tape.

    Bookmark   December 19, 2011 at 5:29PM
Thank you for reporting this comment. Undo
veesubotee

That's fine. What I use are small (flexible) strip magnets.

Makes routine testing easy.

V

    Bookmark   December 20, 2011 at 1:17PM
Sign Up to comment
More Discussions
Neighbor Finally Upgrades to Heat Pump
My next door neighbor finally took my advice and upgraded...
newtalk2
Greenspeed, is this setup ideal/ worth it?
I am building up on my house (cape style) in Long Island...
David
auxiliary heat vs. emergency heat
Greetings, I have a Bryan Evoltion Control heat pump...
decadent
New Mini Split Designs for 2015
I, and I am sure others, would love to hear what is...
josey11
HVAC question
I live near Charlotte NC and have a new Bryant Hybrid...
gtodd1966
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™