Desirable Water Temp for Baseboard Heat

garojNovember 6, 2007

I just had a plumber add baseboard forced hot water to an addition, tying in to an existing zone. I have a gas boiler heating only baseboard (not hot water for shower, etc). While going over the job he noted that my boiler was set for about 185 deg, but he said that for every 10 deg lower you save 3% in energy costs. And he lowered the temp. (I can change it). Is that true? He set it down to about 140deg. I'll see, but imagine the circ pump will run constantly now.

Thank you for reporting this comment. Undo
Brewbeer

I don't know about your specific situation and the 3% claim for a 10 degree decrease, but it is true that the lower you can run the water temp, the cooler the boiler will run, theoretically resulting in cooler exhaust gas temperatures, which means less heat goes up the "chimney", meaning more heat stays inside the house.

    Bookmark   November 7, 2007 at 8:03PM
Thank you for reporting this comment. Undo
braytonak

The circulator may run more often, but it's better than the boiler ramping all the way up to 185° if the house can maintain temperature with the 140° water running more. A boiler that runs more is going to be more efficient because it will spend less time re-warming the water that cooled down while waiting for the next call for heat, which causes it to have to flame up longer to reach the water temperature set point again.

If your boiler is cast iron, 140° is a safe minimum.

    Bookmark   November 7, 2007 at 10:29PM
Thank you for reporting this comment. Undo
baymee

Generally a boiler is set at 160 LOW and 180 High on the aquastat, with 150 being the Low for cast iron radiators.

    Bookmark   November 8, 2007 at 1:21PM
Thank you for reporting this comment. Undo
garoj

Thank you. That is very interesting. The burner is a Burnham Series 2A gas boiler. It seems the circulating pump would use up a significant amount of electricity but maybe not. I appreciate the comments; more welcome.

    Bookmark   November 8, 2007 at 8:46PM
Thank you for reporting this comment. Undo
tmajor

You are going to have to do some research and/or experimenting.

Heat usually transfers best with larger temperature differentials. As an example: An ice cube will melt much quicker with ambient at 100 degrees, as opposed to ambient being 35 degrees. Heating is the same deal .. heat transfer. Of course, some will transfer up the chimney, too. The boiler will always be controlled within an envelope, so that it's extremes will always be within 20 degrees (or whatever), of each other.

    Bookmark   November 8, 2007 at 9:11PM
Thank you for reporting this comment. Undo
baymee

A Taco 007, which is a common circulator, uses a fraction of 1 amp of electricity, maybe about as much as a 50 watt light bulb when it's running.

    Bookmark   November 9, 2007 at 5:46AM
Thank you for reporting this comment. Undo
bonanza_stu

Your water temperature should be the lowest possible to heat your home on a cold day. Some boiler systems use an outdoor reset that can vary boiler water temperature as outdoor temperature changes. If you use an outdoor reset and have a conventional, non condensing, boiler, you should install a thermostatic bypass to prevent the boiler from condensing with low water temps.

    Bookmark   November 13, 2007 at 10:25PM
Sign Up to comment
More Discussions
Enery efficiency of exposed ductwork?
What are your thoughts on the energy efficiency of...
ccintx
Carrier Greenspeed 25VNA Massachusetts Cold Weather Data
Hello Everyone, I wish I had had this information prior...
Sabs83
Need help choosing an efficient HRV Air Exchanger
Hi, My house as a total area of 2300 square feet (1150*x)....
Jim_Lafleur
Geothermal vs Carrier Greenspeed
I am looking to replace my current Heatpump. I have...
mkrafczyk
Mike_home, is this a good idea? re: thermostat
@mike_home, You wrote this back in 2012 and I just...
cindywhitall
© 2015 Houzz Inc. Houzz® The new way to design your home™