insulated flex duct versus galvinized pipe

arliedogNovember 28, 2011

My heating ir conditioning system is in a finished basement. Currently there six inch galvinized pipe runs to all the floor register coming off a galvinized trunk. The longest run to a register is about 12 feet. Is there any advantages or disadvantages for replacing these runs with insulated flexible duct? Having some issues with the current galvinized pipes doing a little popping and cracking during each heat cycle.

Thank you for reporting this comment. Undo
countryboymo

I like the insulated board duct for the main trunk sections and galvanized pipe for the runners to help with noise control. I think the cfm rating on the flex duct is lower than galvanized. Insulating the galvanized would help with the noise I would think. I waited and found some rock bottom specials on insulated flex duct and removed the duct portion and insulated my galvanized runners much cheaper than buying insulation solely for galvanized.

I think the loss in air flow with flex is pretty high in comparison.

    Bookmark   November 28, 2011 at 11:21PM
Thank you for reporting this comment. Undo
energy_rater_la

"I think the cfm rating on the flex duct is lower than galvanized. Insulating the galvanized would help with the noise I would think"

to move the same air that a hard pipe duct with flex the flex is sized one size up.
look at labor cost to install insulation on hard pipe
vs flex.

not poking @ you countryboy...just how my mind works.
how can I get same performance for lesser cost.

of course all should be mastic sealed...long seams,
joints & 90's in hard pipe PRIOR to insulating externally.
with flex it is the take off @ plenum and where flex connects to supply box. other areas to seal are plenum connections, returns and always hole in floor/ceiling/wall
where supply box attaches supply grill.
mastic mastic mastic...always seals, lasts for years
and pays back..in a very very short time.

best of luck OP
and hey countryboymo..things going ok in your part of the world?

    Bookmark   November 30, 2011 at 7:55PM
Thank you for reporting this comment. Undo
arliedog

After info here and further investigation on line seems like sticking with my galvinized pip is the best. Have done some tweaking on how the pipe is hung as well as clearances and have resolved some of the popping and cracking issues. Thanks for all inputs.

    Bookmark   December 1, 2011 at 8:58AM
Thank you for reporting this comment. Undo
spf5209

arlie - I saw your other thread as well. I am having airflow noise issues with my system. Why did you decide against insulated flex? Thanks.

    Bookmark   December 11, 2011 at 11:20AM
Sign Up to comment
More Discussions
Pls tell me the best uses for Carrier Air Handler Model # FV4CNF003
Hi GW, I am stuck with a new 2012 air handler/heat...
ontariomom
Baseboard heater thermostats
We are looking to install (2) 120v baseboard heaters...
stephja007
Need help choosing an efficient HRV Air Exchanger
Hi, My house as a total area of 2300 square feet (1150*x)....
Jim_Lafleur
Insulating floor on my raised home in Louisiana.
We recently installed solar panels on our home. We...
ktyler1320
Geothermal vs Carrier Greenspeed
I am looking to replace my current Heatpump. I have...
mkrafczyk
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™