Skeptical HVAC Issues

Moparman915October 2, 2012

Hey all,

I am looking for some advice for an HVAC issue that I have been having at one of my rental properties. I am pretty well educated on the nomenclature and process for A/C systems, but am not up to speed on pricing and proper diagnostics.

My tenant told me in August that the A/C was freezing at the condenser, at which point I had contractor #1 take a look at it. He replaced the transformer/capacitor and added 1.2 lbs of R-22. A/C worked for a week and the problem recurred. Got a refund because the "repair" failed.

Contractor #2 found that the R-22 was a little low and added 1 lb, but saw no evidence of leaking. The A/C worked for about 2 weeks, but the system stopped outputting cool air.

Contractor #3 had fluctuations on his gauge so he sensed a leak or a bad metering device. He seemed very knowledgeable and I decided he�d be best suited to perform a leak check on my system. He performed a triple evacuation of the refrigerant to 500 microns and checked for leaks/noncondensables.

(cost $652)

There were not leaks discovered and he recharged the system. This worked for about a month.

He had a tech come over and diagnose the system again. This time they replaced the capacitor because it was reading low. No fix, but we are having a different problem, and I am ready to ditch this guy all together. Here is what contractor #3 says in an email:

"I just got a call from the distributor. They had to look up your coil info with the factory since its not made any more..it looks like that coil didn't come with a TXV..and for it to behave the way it is means basically that we caught the air in the refrigerant lines too late.

We may be able to replace the coil and flush the refrigerant lines...but if the compressor was too damaged and has shavings breaking off into the lines that may need to be replaced too. It was suggested that we perform an acid test and megohm the compressor to try and determine AC longevity since the system is a bit undersized"

After telling him that only the fan was working(blowing ambient air and not cool air at all), this is what he said:

"When I first put my gauges on yesterday it was acting low on charge..then it acted like a Txv open and everything went normal for an hour or so. Then before I called you it seemed as a valve had closed causing really low suction pressure and high head pressure @ the same time.

I had told him to not use the AC and run fan only or set stat to ac and kill Pwr to AC unit for full fan speed ti prevent further damage.

I live in a house where my system is 3/4 ton undersized..for now it work ok...but when it starts giving me problems I'm just going to replace it all with high efficiency stuff properly sized.

I know were looking @ at least replacing the coil...possibly the compressor or condenser. It may be a good time to upgrade the system but that would require increasing the cfm by doing the furnace @ the same time. And that's your call. @ this point no matter the choice..we have to evacuate the refrigerants again. But if you upgrade the system we can credit the work we've already done to help out a bit.

Sorry for the novel, but I really would like some input from the community. I have the feeling that contractor #3 is trying the old "hook-line-and �sinker" method with trying to get me to pay for a complete system.

Any thoughts? Thanks in advance!

Chris

Thank you for reporting this comment. Undo
mike_home

I think you have a leak. Contractor #3 can't seem to find it and is now taking you down a path where will spend a lot of money replacing parts until you give in an replace the condenser and coil. He is also looking at replacing the furnace for what seems to be a bogus reason.

How old is this unit? It may make more sense to put in new equipment rather than deal with techs who can't find the problem.

    Bookmark   October 3, 2012 at 8:37AM
Thank you for reporting this comment. Undo
harlemhvacguy

Where did you find these contractors? Under "F" at the BBB?
Listen...... to be honest with you, you have had so many people working on it, doing so many different things, there is no telling what the real problem is now.

What size unit is it? 1 pound low is not so low it would make it freeze so bad.

Does it have a txv or does it not have one?

A freezing up unit will have little to nothing to do with the outdoor unit.

Are you sure the evaporator is clean? Filter clean? Has any one of the contractors verified this?

Units freeze up due to lack of airflow,lack of load, low on refrigerant, or restriction in system. I don't think any of them know which it is.

    Bookmark   October 3, 2012 at 2:48PM
Sign Up to comment
More Discussions
Neighbor Finally Upgrades to Heat Pump
My next door neighbor finally took my advice and upgraded...
newtalk2
2 Stage vs 1 Stage
I am trying to decide what HVAC replacement system...
cms9323
Enery efficiency of exposed ductwork?
What are your thoughts on the energy efficiency of...
ccintx
Need help choosing an efficient HRV Air Exchanger
Hi, My house as a total area of 2300 square feet (1150*x)....
Jim_Lafleur
Is 16 SEER Lennox A/C 5X better than 18 SEER Goodman?
I bought a bank repo home 2 years ago in San Diego....
davidahn
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™