oil furnace excess air reading

flamingo33October 25, 2012

My York oil furnace has an excess air reading of 3l% with fan OFF and 49% with fan ON. Other specs: draft .02-.04, smoke 0, CO2 9.1, efficiency 82%. Testo 327-1 combustion analyzer used . CO readings are: Fan OFF, 6ppm, 8ppm CO AirFree; Fan ON, 9ppm, 14ppm CO Airfree. My oil tech says EA fluctuation alone indicates possible cracked heat exchanger or leaking/warped gasket, furnace should be replaced. Two other independent techs did a visual and scope inspection, said furnace could be used safely. How important is the EA reading? The furnace is 25 years old, gently used in small house, no oil smell when coming on, no soot, no noise. Who do I believe? Thank you for your help.

Thank you for reporting this comment. Undo
bus_driver

I have no explanation for the difference in the readings. But if there is no smell and no soot, a cracked heat exchanger or bad gasket is unlikely. Is the furnace getting combustion air from the conditioned space?

    Bookmark   October 25, 2012 at 4:36PM
Sign Up to comment
More Discussions
Pls tell me the best uses for Carrier Air Handler Model # FV4CNF003
Hi GW, I am stuck with a new 2012 air handler/heat...
ontariomom
New Mini Split Designs for 2015
I, and I am sure others, would love to hear what is...
josey11
Mike_home, is this a good idea? re: thermostat
@mike_home, You wrote this back in 2012 and I just...
cindywhitall
Heat pump choices for first timer. Advice??
Hello, First post, great place you all have here. We...
adayrider
Need help choosing an efficient HRV Air Exchanger
Hi, My house as a total area of 2300 square feet (1150*x)....
Jim_Lafleur
© 2015 Houzz Inc. Houzz® The new way to design your home™