Help with HVAC estimates

elaineycabaneySeptember 6, 2012

Quotes for my 1300 sq ft single story Brick 1928 home. Old windows and insulated attic only:

CONTRACTOR #1

A) Goodman GSZ13036 (heat pump)

Goodman CHPF36

Goodman GKS9090 (furnace)

Size KW

BTU/SEER rating 3 ton/13 seer

Programmable Edge thermostat

Hybrid Heat Pump

Total: $5383

B) Carrier 25HBC336 (Heat Pump)

Carrier CNPHP36

Carrier 59SC2A080 (Furnace)

Size KW

3 ton/13 seer

same thermostat as above

Hybrid Heat Pump

Total: $5948

Both include the following:

PVC drain/new pad/new copper lineset/reconnect ductwork to new location in basement/add air filter at unit/reconnect fuel piping/PVC Flue/Reconnect control wiring/Install new Power wiring at indoor breaker box/Mechanical & Electrical permit/Add supply in Kitchen.

CONTRACTOR #2

Amana Model #'s AMH 950703B and CAPF3131B

Seer 13/EER 11.0/AFUE 95%/Btuh Cooling 30,000/Btuh Heating 70,000/CFM 1000

Installation shall include:

Install 2.5 ton a/c wth 70,000 btu natural gas (needs to be converted to propane) furnace and matching A/C coil.

Repair duct work where package unit is, tied in and seal.

Run new line set-flue-thermostat-equipment pad-duct transitionsand labor to complete job.

new low voltage wiring/new reinforced equip pad/new vibration isolation pads/new properly sized refride suction line(s)/evacuate refrig system/charge to manuf. specs/new copper wire/install energy saving thermostat/make air tight plenum transition/new gas piping from existing to unit/new vent pipe & cap/new condensate drain system.

Total $4,500

(I don't believe he figured on relocating the shutoff to the new indoor breaker box...do you think that it's necessary? He also thought that the current 3 ton gas pack unit was oversized. and he'd reinsulate all ductwork. He did not add the new vent for kitchen in his estimate which I will ask for.)

CONTRACTOR #3 never called back, jeez.

Thanks in advance for any advice and questions I should be asking.

Thank you for reporting this comment. Undo
elaineycabaney

To Clarify:
I live in SC and use propane fuel. Current system is a 3 ton Gas Pack and the compressor is worn out. I have r30 batts in the attic. The contractor didn't realize that he couldn't add soffit vents due to lack of space and the brick exterior. So I have a ridge vent and two gable end vents. I do need additional venting and will most likely add an electric powered gable end fan.

    Bookmark   September 6, 2012 at 6:24PM
Thank you for reporting this comment. Undo
elaineycabaney

Here are the load calculations that I did on loadcalc.net (thanks for the tip, garden webber) for a Below Average construction regarding tightness (R30 in attic, brick exterior walls w/o insulation, single pane windows with storms)

Total BTU's Cooling: 37006
Total BTU's Heating: 43690
Sensible Load: 33364
Laten Load: 3642

See original posting on 9/6/12 for estimates received, I am also waiting for an American Standard certified installer for a quote, any recommendations are appreciate. My house always smells stale and I noticed there are air filtrations system, however, I am on a budget and don't plan to stay in the house more than three years. Thanks in advance for any suggestions.

    Bookmark   September 12, 2012 at 2:45PM
Sign Up to comment
More Discussions
Need help choosing an efficient HRV Air Exchanger
Hi, My house as a total area of 2300 square feet (1150*x)....
Jim_Lafleur
can people share their weekly propane use and square footage, please?
With the coldest weather in roughly 20 years here,...
davidrt28 (zone 7)
carrier infinity with greenspeed service settings
We just built a new home in central Kansas this year,...
Energywise.ks
Heat pump choices for first timer. Advice??
Hello, First post, great place you all have here. We...
adayrider
Can a house and cottage share a condenser?
I have a house (1000sf) and cottage (440sf) with about...
aptosca
© 2015 Houzz Inc. Houzz® The new way to design your home™