Correct size flue for Furnace and water Heater?

yazkSeptember 24, 2010

Hello,

I have a Gas furnace and a Gas water heater that each have a 4" flue pipe from them. These two are then connected into a single 8" pipe that goes up through my chimney. I was told that 8" is too large and it has probably been there for years and no one bothered chnaging it when they installed the new furnace.

Can anyone confirm what size flue I should use to cater for two 4" pipes?

Thank you for reporting this comment. Undo
kalining

Look in the flue sizing tables in the gas code. Depends on your total BTU output.

    Bookmark   September 24, 2010 at 1:06PM
Thank you for reporting this comment. Undo
zl700

And since your furnace is 4" it sounds like a fan assist so you should be looking at the NAT + Fan total BTU chart with correct vent connector length and chimney height.

Heres a link why there needed and sizing charts, assuming its gas appliances

http://www.mtlfab.com/media/L1238.pdf

    Bookmark   September 24, 2010 at 11:26PM
Sign Up to comment
More Discussions
New Bryant legacy vs 5 year old carrier infinity
My parents need a new a.c., There's is broken and probably...
David
Navian condensing combi, good or bad?
Hi, I am looking into converting from oil to gas and...
rickyk22
wood stove insert causing boiler to cycle?
We have an oil-fired boiler, an indirect water heater,...
kitasei
Neighbor Finally Upgrades to Heat Pump
My next door neighbor finally took my advice and upgraded...
newtalk2
foul smell from gas furnace vents
Please help. We have a gas furnace (only 2 years old)...
taracol
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™