I'm making some improvements to my noisy and undersized ductwork, and seeing big improvements to the areas I have done so far.

The next step is to install a correct plenum and ducts to a family room that is over a crawl space, which has a very inadequate system. My plan is to used insulated flex duct, connected directly to the furnace plenum, starting at 10" diameter, and running it through this space, wyeing off 6" ducts for individual registers along the way, and reducing the diameter of the main plenum along the way. Similar to the attached picture. The rest of the house is supplied by a traditional rectangular main trunk off the opposite side of the furnace plenum.

I'm trying to follow good duct design practice as I've learned by reading, but something mystifies me. In a rectangular trunk installation, we are told never to install a branch duct off the very end of the trunk, but when I see diagrams of reducing trunk systems, there is a takeoff off the end.

What exactly is the reason for not taking a branch duct off the end of an extended plenum? And why does this rule not seem to apply to a reducing trunk layout? I want to do this right, assuring the best airflow and least noise.

Any opinions?

Thanks!

David

Thank you for reporting this comment. Undo
energy_rater_la

no pic attached.
you don't tap off the end of the supply plenum
because it reduces static pressure.
as the air enters the plenum it hits the end cap
if a duct is taken off the end cap the total pressure
is reduced.

also you don't tap off the plenum within 18" of the coil
not sure why...but just one of the things I was taught
in class.

10" to tri box then 6"? you sure about those sizes?
6" is usually a bathroom. do you have a ductalator to
know how many cfm of air each size duct can move?
this along with room size determines how much cmf
to provide. then you can divide it between two ducts.

that pic would help.

make sure you mastic seal all duct take offs, where
flex connects to supply boxes, where supply boxes
penetrate floor & plenum to equipment connections.
duct leakage in a crawl space creates a lot of problems.

best of luck.

    Bookmark   September 28, 2012 at 11:18AM
Thank you for reporting this comment. Undo
brickeyee

" don't tap off the plenum within 18" of the coil
not sure why"

You do not want to increase flow velocity over the coil.

It reduces effectiveness and efficiency.

    Bookmark   September 28, 2012 at 1:04PM
Thank you for reporting this comment. Undo
brickeyee

Uniformity of flow can also be disturbed.

    Bookmark   September 28, 2012 at 1:05PM
Sign Up to comment
More Discussions
Central Air OR Mini-Split
Hello everyone, We bought our house 2 years ago (1938...
Bongo
gas wont come on. forced air gas fired furnance
the Furnace was starting then running a couple minutes...
waterguytexas
Is this HVAC system OK?
Replacing original old ~9 seer unit. House is 2001...
thereloader
Blown in insulation vs spray foam
I am looking for advice. I have a home built in 2000...
mkrafczyk
Are mini-splits a bad idea.
I have lived in both Europe and the Middle East and...
bry911
Sponsored Products
Nourison Splendor Hand-tufted Beige/Black Rug (7'6 x 9'6)
Overstock.com
Gramercy Brown Rectangular: 5 ft. x 8 ft. Rug
$449.00 | Bellacor
Gray 69" modern sofa
Interior Define
Lemon Twist Apothecary Table Lamp
$99.99 | Lamps Plus
Barrique White Set Of Four Wine Glasses
Classic Hostess
Round Metal Cotton Balls Jar Made in Brass
TheBathOutlet
Masiero Lighting | Eva Table Lamp
YLighting
Heaven & Earth I Table Lamp by Fire Farm
$291.60 | Lumens
© 2015 Houzz Inc. Houzz® The new way to design your home™