Change over valve setting

langle1033August 17, 2009

In Honeywell Vision Pro 8000 (TH8320U1008) setting menu, I have to select either cool (=0) or heat (=1) for the change over valve.

I have a heat pump with electric backup (upstair) and a heat pump with gas back up (downstair).

Please tell me how to setting this parameter for each unit.

Thank you

Thank you for reporting this comment. Undo
weedmeister

It differs by manufacturor. Who makes your two units?

    Bookmark   August 17, 2009 at 3:54PM
Thank you for reporting this comment. Undo
langle1033

Both of my heat pump units are Goodman.

Thank you

    Bookmark   August 17, 2009 at 4:56PM
Thank you for reporting this comment. Undo
refrigman1

You should select 0. The reversing valve needs to be energized in cooling.

    Bookmark   August 17, 2009 at 8:33PM