2 air conditioning units for new build

lniaJuly 6, 2012

Hello

We are building a new home and will be installing 2 air conditioning units. 1st floor is slightly over 1900 sq feet with 2 story great room. 2nd floor is approximately 2100 sq feet if we include bonus room. Is there a rule of thumb regarding tons for each floor of the house? Is it better that the higher tons cool 2 nd floor? I appreciate any advice or points we should consider as this is all new for us.

Thanks

Thank you for reporting this comment. Undo
mike_home

The HVAC contractor needs to calculate the heating and cooling load for the home. This is referred to as a Manual J calculation. Rules of thumb lead to equipment which is either over sized or undersized.

The cooling load will usually be higher for the second floor. But you could have a large amount of south facing windows on the first floor which could make the cooling load higher than the second.

    Bookmark   July 6, 2012 at 5:38PM
Thank you for reporting this comment. Undo
david_cary

It really is west facing windows rather than south that is the issue. The manual J that I used has east and west windows as identical which is just wrong but that is what it used. I find that 2nd stories tend to have lower needs because of smaller windows which dominates over heat rising. Unless the ductwork is in the attic, which adds a lot of heat so then the 2nd story unit creeps up in size.

    Bookmark   July 7, 2012 at 5:03AM
Thank you for reporting this comment. Undo
lnia

We will hAve 2 furnaces as well. One will be in the basement. One will be on the 2nd floor bonus room. Our house faces west. I would say our largest windows are on the 1st floor (I'd patio door, dining room window, den window,etc). Is it possible for a layman to do the manual j calculation?

    Bookmark   July 7, 2012 at 7:40AM
Thank you for reporting this comment. Undo
david_cary

Yes a lay person can do a manual J but you have a lot of inputs and need to know a lot of details. Why are you sizing this yourself or are you just checking the contractor's work?

In some jurisdictions, a manual J is required with the permit. I will say that doing a manual J and following one are not the same thing.

You will tend to piss off HVAC contractors when you do your own manual J or disagree with their's. They want to oversize in their DNA and it is very difficult to break that. Ask me how I know.

For a manual J, you need all the wall measurements, window sizes, r and u values, SHGCs for the windows, overhangs on windows. You have to speculate what the air leakage rate is although it isn't very exact. You need to know where the duct work is located.

    Bookmark   July 8, 2012 at 4:34AM
Sign Up to comment
More Discussions
Need help choosing an efficient HRV Air Exchanger
Hi, My house as a total area of 2300 square feet (1150*x)....
Jim_Lafleur
Problems with HVAC in 1958 Cape Cod
I've been reading the blogs here and hope that the...
ginaff58
Mike_home, is this a good idea? re: thermostat
@mike_home, You wrote this back in 2012 and I just...
cindywhitall
New Furnace - Keep Previous Excellent Thermostat?
I am replacing a 20-year-old single-stage Carrier gas...
ak0402
In Floor Radiant Heat for Two Story
My husband and I are buying an old house with radiators....
kmosbacher
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™