3 ton versus 3.5 ton

tecopa03June 24, 2008

I'm having bids done on my house to replace a 12yr old HVAC system for my 1200sq foot house.

My original split system was a 3.5 ton installed in 1996. The two bids I've had so far say a 3 ton would be more than enough.

Does this make any sense, and are newer systems that much better than a 12yr old system?

Thank you for reporting this comment. Undo
ryanhughes

What's your location? A heat load calculation is the only way to determine the proper sizing for your home--I wouldn't accept any other method. 3 tons still sounds huge for 1200 sq. ft. I have 3.5 tons doing around 3500 sq. ft. (incl. finished basement) at my house with no real issues--cools to 72* even in the 90s. Heat load calc is the answer to your question. : )

    Bookmark   June 24, 2008 at 11:04PM
Thank you for reporting this comment. Undo
ky114

What they're probably telling you here is not that the new system is better but that your old system was oversized, and on the surface of it that seems like a possibility, since 3.5 tons is a lot for 1200 square feet in most cases.

Someone is going to tell you to have them due a Manual J load calculation, and that's certainly good advice, but for the sake of discussion, how much does your current system run to keep the house cool on the hottest days? If your old system is running all day on the hottest days, you may have a house with high heat gain (possibly older construction, many windows, or high internal heat gain from living activities). But if your current system has run intermittently even on the hottest days, and I'm guessing that's the case, you probably have room to reduce the sizing, and this would give you better humidity control and reduce energy consumption.

    Bookmark   June 24, 2008 at 11:09PM
Thank you for reporting this comment. Undo
tecopa03

I live in Las Vegas but have been assured that a 3 ton unit is just right for my 1200sq foot house. My current 3.5 unit, during really hot days stays on between 20-30 minutes, turns off between 5-10 minutes. And the house really doesn't stay that cool (duct work is fine).

And from what I've been reading, it is/was typical for house manufacturers to put in a HVAC system that is 1/2 to 1 ton bigger than necessary.

So I'm starting to think that a 3 ton unit would be best, and I understand the Manual J cal would be best for anyone.

I'm also looking at the 3 ton Lennox XC21. Does anyone use this unit and what do they think?

    Bookmark   June 25, 2008 at 12:11AM
Sign Up to comment
More Discussions
HVAC billing question
Question for the pros...... So I had a faulty capacitor...
spe720
How to heat this room?
Hi folks! First post in this forum. I live in ec Iowa....
sparky_10
Need help with selecting Eff Heat Pump replacement.
20 yr old American Std Heat Pump stopped working. ...
2015hvac
HVAC design
In determining the HVAC system to use in our new construction,...
bethmcg
No Fully Trained Mini Split Installers
Reading threads about mini split heat pumps I got curious...
nerdyshopper
Sponsored Products
Home Decorators Accent Rug: Ultimate Shag Black 2' x 5'
$89.00 | Home Depot
Elk Lighting 19.5H in. Ruby Vase - 93-5860
$114.00 | Hayneedle
UniFlame 3 Panel Versailles Fireplace Screen - S-9668
$321.00 | Hayneedle
Gold Accent Lamp: 16.5 in. Gold and Bronzed Pot Lamp 07M559
$99.00 | Home Depot
Dahlia Double-Tiered Outdoor Side Table - Black, 18" Round, Patio Furniture
$549.00 | FRONTGATE
Aqua Cil Floor Lamp by Artemide
$1,550.00 | Lumens
Sunnydaze Mediterranean 4-Tier Water Fountain, 49 Inch Tall
SerenityHealth
Cold Cross Handle Angle Stop - 5/8" x 1/2" OD Compression
Signature Hardware
© 2015 Houzz Inc. Houzz® The new way to design your home™