HVAC outside unit not working

sn002June 30, 2012

My unit is 10 years old. The outside unit won't start so I did a little research

to find out the contactor didn't close by itself when I turned on the thermostat to cool.

I went a head and replaced the new contactor. Now it is closed by itself when I turned on the unit. But it is still did not work. All I heard was like a brief humming sound and the fan did spin just a little bit then stopped. The inside unit is working fine...the blower blows out air but not cool air. Please advice. Thanks

Last year I put in a new capacitor everything working fine until today. so I believe the capacitor is fine.

Thank you for reporting this comment. Undo
mike_kaiser_gw

Are you sure all the wires are in the correct place? You've checked to ensure you are getting 240v to the contactor and beyond? With 240v you should get 120v between each hot wire and ground and 240v between the two hot wires.

    Bookmark   July 1, 2012 at 6:27AM
Thank you for reporting this comment. Undo
sn002

Here is how I tested the contactor. Turned on the unit from the thermostat to energize the coil so the contactor closed.

I got 24v on the contactor coil voltage. Got 240v on the bottom hot wires incoming power from the disconnect box. Got 240v on the other end of the contactor (coming out). Got 0v from each bar of the contactor so that means they are closed circuit. Got 120v between each hot wire (in/out) and ground.

I got a different reading if I tested without turning on the unit from the thermostat.

One question though. What is the correct way to test the contactor with or without the unit on?

    Bookmark   July 1, 2012 at 9:49AM
Thank you for reporting this comment. Undo
mike_home

Don't assume the capacitor is good because it is a year old. New capacitors have been known to fail prematurely.

    Bookmark   July 1, 2012 at 10:20AM
Sign Up to comment
More Discussions
New HVAC install in So Cal
Hi Everyone, I just got a quote from Home Depot contractor....
revlimit
Maytag/Nordyne/Nortek HVAC
Wanted to share my HVAC experience. Hopefully save...
bgfuller
Has anyone found solution to HVAV Dirty Sock Syndrome
Two years ago I had a Trane heat pump installed in...
idreos
HVAC design
In determining the HVAC system to use in our new construction,...
bethmcg
Opinions please Mitsubishi M - S E R I E S H I G H P E R F O R M A N C
Our HVAC guy is suggesting this for a complete system...
almostemptynester
Sponsored Products
Heart Petite Pie Mold
$6.99 | zulily
Bourges 24-inch Round Mirrored Metal Accent Table
Overstock.com
Kichler Bronze 3-LED Hardscape Light with Mounting Bracket
$89.40 | Lamps Plus
'You're My Favorite Work of Art' Display Board
$19.99 | zulily
Home Decorators Indoor/Outdoor Area Rug: Home Decorators Collection Rugs
Home Depot
Outdoor LED Battery Powered Motion Activated Wall Sconce
$59.91 | Lamps Plus
Contemporary Indoor/Outdoor Area Rug: LR Resources Rugs Dazzle Brown 5 ft. x 7
Home Depot
Wingfield Game Table
FRONTGATE
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™