Window AC not cooling properly

mwkbearJune 28, 2007

Hi,

I have an older window AC unit which was left by the prior owner of my house. It's a Carrier unit, 8800 BTUs.

It's in a main floor living room, approx. 325 Sq. Ft. The room doesn't really seem to be getting cool on these hot days we've been having. Even with the thermostat turned to maximum cool, and the room being pretty warm, I hear the compressor cycling on and off. When it's on, the air coming out is icy cold but it only seems to be on about half the time.

Is this a thermostat issue? Is it something somewhat simple to fix maybe? The unit is sort of built into the window, and I hate breaking it out to put a new one in, if it's just something simple or easy to fix.

Thank you for reporting this comment. Undo
davidandkasie

sounds like the thermostat probe is getting cold and forcing the ac to turn off. i have had that happen before. pull hte front off the unit and you will see a copper tube attached to the coils. pop it out gently and move it lower on the coil.

also make sure the coils are clean, both inside and outside. for the outside coil, spray it with a water hose to wash it out, the dirt is on the inside so it usually is not visible unless you totally disassemble the unit.

    Bookmark   June 28, 2007 at 11:37AM
Thank you for reporting this comment. Undo
mwkbear

Hi,

Thanks so much! I'll try that when I get home and see if it has an effect.

    Bookmark   June 28, 2007 at 12:16PM
Thank you for reporting this comment. Undo
garyg

Filter - what does the filter look like - may need to be replaced.

    Bookmark   June 28, 2007 at 1:46PM
Thank you for reporting this comment. Undo
cimberlie_desade

We are having the same problem with our older "WallMaster" unit by Friedrich. After cleaning both coils, filters, checking thermostat, etc finally broke down and called in a repair person. Sad news was that the compressor is going causing the unit to shut down before reaching the proper temperature.

Try all the above suggestions, especially cleaning the filter, and a through cleaning of the units coils (both).

Get a good thermometer (an instant read kitchen one will do), and check the difference between the incoming air (front of the unit), and what is being blown out. There should be at least a 12-20 degree difference. If the condenser comes on, but shuts down after about 10 minutes, you may have a problem with motor (condenser), in which case it would be cheaper to chuck the unit and buy new.

In fact considering how inexpensive units can be,you may wish to look into getting a new one sooner rather than later. The last thing you want to do is purchase a new unit during a heat wave because your current AC died a slow painful death. If funds are tight check Craigslist for local people selling units. They may not be what you want, but it will get you through the summer, that way you can wait and get a good deal when stores are clearing stock in the late Fall.

    Bookmark   June 28, 2007 at 3:14PM
Thank you for reporting this comment. Undo
dadoes

There should typically be foam strips either on the backside of the front grille or around the air discharge area to keep the cold outflow separated from the intake. If the foam is deteriorated or missing, cold output air can get sucked or directed back into the intake *behind* the grill which also will give the thermostat a false reading and cause short-cycling.

    Bookmark   June 28, 2007 at 4:10PM
Thank you for reporting this comment. Undo
bob_brown

All motors use a capacitor and some kind of start relay if 110vac. This is similar to what a refrigerator uses. When the cap, relay or overvoltage is bad, it can short cycle or shut down until the compressor cools enough to allow it to restart.

Cleaning coils on a window unit requires dissembly of the unit. The inside of the outer coil needs to be cleaned, and the outside of the inside coil needs to be cleaned. I have seen dirty evaporator coils inside of the hidden part of the inside or evaporator coil many times. This normally requires dissembly of the cover plates to reach the coil. The outdoor coil will get heavy dirt buildup in the corners. This hurts the efficiency enough to shut down the compressor or even trip the circuit breaker.

In the past, when I cleaned a window unit, I liked to use the rear of the pickup. It was high enough that I did not have to bend over, and I could get water on the bed without damaging the truck. I liked to turn the AC unit on it's side to clean the pan. I like to allow a day or so to dry, and for the oil to settle inside of the compressor.

    Bookmark   June 29, 2007 at 2:30AM
Sign Up to comment
More Discussions
Is this HVAC system OK?
Replacing original old ~9 seer unit. House is 2001...
thereloader
Heat Pump.....will it really save me money?
I recently moves into a new house in Mass, a 1650 sq...
Jinx_1832
Heat Pump in Northern Virginia
Does anyone have advice on which contractors may be...
jbedford004
Replacing heat pump and keeping current air handler....
Well the good news is we are being blessed with a new...
piratechick
New HVAC install in So Cal
Hi Everyone, I just got a quote from Home Depot contractor....
revlimit
Sponsored Products
Indoor Fan and Light Kit: Hampton Bay Florentine IV 56 in. Brushed Nickel Ceilin
$99.00 | Home Depot
Sanded gold poeta prisma picture frame
Origin Crafts
Urban Swag Pendant
Lightology
Craftsman Single Panel Fireplace Screen
Signature Hardware
Bruck | 36 Inch Enzis Kit
$498.75 | YLighting
Mad Meditations Art Print
$34.99 | Dot & Bo
© 2015 Houzz Inc. Houzz® The new way to design your home™