Hard start kit

barrychanJune 1, 2012

hi all!

My condenser unit (Carrier 38TKB036) for the past year has been having trouble starting. The fan would start but the compressor would not kick in until say half an hour later. The first two years it didn't have that problem only recently. I have a dual capacitor that I replaced and it did not solve the problem. I am looking into the hard start kits below but they call out a separate 'run' and 'start' capacitor. So does that imply I only need to purchase the relay from the kit or I have to change out my dual capacitor that is in there right now? Thanks for the attention.

http://www.captiveaire.com/CatalogContent/Fans/Sup_MPU/doc/Start Capacitor Relay Kit.pdf

Thank you for reporting this comment. Undo
handy-man

Barrychan,

Since you have a 3 ton unit. Get this hard start kit. It comes with a relay.

http://www.amazon.com/Compressor-Saver-Hard-Start-Capacitor/dp/B003FNMADE/ref=pd_sim_sbs_hi_2

The instructions are easy.

    Bookmark   June 1, 2012 at 8:48PM
Thank you for reporting this comment. Undo
mike_home

The hard start kits come with a start capacitor and relay. You need both items in addition to the run capacitor. The capacitor in the kit is wired in parrallel with the run capacitor for the compressor. The relay disconnects the start capacitor once the compressor starts up. This is important since the start capacitor will not allow the compressor motor to run correctly once it is started.

The 5-2-1 compressor saver is easier to install and seems to be popular with HVAC techs. Here is a link the web site. There is a good video explaining the installation and operation.

Here is a link that might be useful: 5-2-1 compressor saver

    Bookmark   June 2, 2012 at 5:02PM
Thank you for reporting this comment. Undo
barrychan

Thank you all for your responses. I'm still a little confused since I have a dual capacitor. does that mean it is both a run and start cap? And will i just use the relay from the kits you recommended?

Thanks!

    Bookmark   June 2, 2012 at 10:48PM
Thank you for reporting this comment. Undo
mike_home

The dual unit has run capacitors for the condenser and the fan. You add an additional capacitor which will be used for starting only.

    Bookmark   June 3, 2012 at 12:07AM
Thank you for reporting this comment. Undo
brickeyee

A hard start kit adds additional start capacitance, ad a timer relay t pull it out of the circuit.

It does not replace or change the capacitors you already have.

    Bookmark   June 3, 2012 at 11:25AM
Thank you for reporting this comment. Undo
barrychan

I got it. Thanks for your patience. Will follow up with the forum once I have it installed to see if the problem went away.

    Bookmark   June 4, 2012 at 8:47AM
Thank you for reporting this comment. Undo
barrychan

Just wanted to let you guys know the hard start kit helped. The compressor is starting faster. The fan still does start for a few minutes before the compressor kicks in but the compressor is starting a lot faster than the usual 45 minutes of waiting that I have been used to. THanks for all the help; you guys are great.

    Bookmark   July 2, 2012 at 10:35AM
Thank you for reporting this comment. Undo
mike_home

It sounds like the condenser does not have much life left. If you make it through this summer, then start planning for a new unit in the spring.

    Bookmark   July 2, 2012 at 1:32PM
Sign Up to comment
More Discussions
Does Air Duct Cleaning really help?
We live in a 40 year old home with a forced air gas...
lincann
company insists on all payment in advance
Having 2 mini-splits installed, have already paid half...
gramarows
Honeywell th6320R Thermostat
My Honeywell TH6320R thermostat (communicating with...
zver11
Disconnect for Fujitsu mini split indoor unit (slim duct type)
We are installing a Fujitsu mini split system that...
ylmzm
New HVAC install in So Cal
Hi Everyone, I just got a quote from Home Depot contractor....
revlimit
© 2015 Houzz Inc. Houzz® The new way to design your home™