I have a lot of air flow from my vents

solrac6262May 5, 2012

Hello all,

I have 3 units in my house, they are 3 1/2 ton.. but since the house was built in 2004 I've been having this excesive amout of air flow from the vents, thats been causing this noisy vent, don't know what to do, dampers?? another guy told me because I need extra return..

what you guys think

thank

Thank you for reporting this comment. Undo
tigerdunes

First , I would want to know what the airflow setting is on the blower motor.

Next size of return(s).

To be clear, you have three 3 1/2 ton systems for a total of 10 1/2 tons?

How many returns for each system and their size?

IMO

    Bookmark   May 6, 2012 at 9:21PM
Thank you for reporting this comment. Undo
solrac6262

thanks
are you talking about the speed? I think is medium
yes I have 3 systems one for the south side of the house and the other for the north side, other unit is for the upstairs rooms .
each system have one small return and a big return like 12" or larger not sure the size

    Bookmark   May 6, 2012 at 11:27PM
Thank you for reporting this comment. Undo
mike_home

Your duct work is probably undersized for the size of your three systems. The supply and the return could both be too small. Adding dampers is not going to solve your noise problem.

How many square feet is the first and second floors? What is your location? Who decided you needed 10.5 tons of cooling?

    Bookmark   May 7, 2012 at 8:20AM
Thank you for reporting this comment. Undo
solrac6262

its a 4200 sq feet home, but shut man probably the upstairs is approx 1500 location is Flower mound TX..
when the house was built, but I think the builder I bought the house a year after the house was built ..
I have a few companies over but they are clueless the last guy was here on saturday charged me a bunch of money to do a tune up on the systems and add freeon 6 lbs for 330 I think he was a theft..

a guy that sells equipment told me that it could be the returns that I probably need it another return, that some times its like when you are blowing on a straw if you make it bigger less the noise..

    Bookmark   May 8, 2012 at 12:23AM
Thank you for reporting this comment. Undo
joe_mn

He put 6 lbs in 1 unit? Was before/after performance different? Did he show you proof of performance change? Is guy a lone wolf or does he work for larger firm? Go after firm or see if you can talk to his supervisor? Could be fraud.

    Bookmark   May 8, 2012 at 5:48PM
Thank you for reporting this comment. Undo
udarrell

10.5-Tons is way too much for 4200-sf home.
That's an average of 400-sf per ton of cooling; under even tough heatload conditions when equipment is working properly 600-sf per ton will nearly always get the job done.

Because there appears not to be enough airflow through the cooling coils it would appear the units are not performing near their Rated Capacities.

All airflow needs to be checked with an anemometer to each room. The duct system should have a Manual d evaluation performed on them to see if they need retrofit work performed on them.

Also, I'd have a Home Energy Efficiency Audit performed on your home & do the cost effective retrofit-work. That should result in a reduction of required Btuh.

Room thermostats with SWING temp setting should be used to get longer runtimes & longer times between on cycles.

Here is a link that might be useful: Correct /sizing of A/C Equipment & Duct Systems

    Bookmark   May 12, 2012 at 3:55PM
Sign Up to comment
More Discussions
Carrier Greenspeed 25VNA Massachusetts Cold Weather Data
Hello Everyone, I wish I had had this information prior...
Sabs83
Greenspeed, is this setup ideal/ worth it?
I am building up on my house (cape style) in Long Island...
David
New Mini Split Designs for 2015
I, and I am sure others, would love to hear what is...
josey11
Problems with HVAC in 1958 Cape Cod
I've been reading the blogs here and hope that the...
ginaff58
Insulating floor on my raised home in Louisiana.
We recently installed solar panels on our home. We...
ktyler1320