veesuboteeMay 3, 2012

I have an RARL (16 SEER) a/c with an RCQD coil and RGFD mod furnace. I chose this coil as I wanted maximum dehumidification as opposed to highest SEER (actual SEER is 14.5).

During installation, the contractor enabled 'HIGH SEER' on the board. I suspect that this increases blower speed (to gain higher SEER) above that set on the board, and thus lowers latent capacity.

Can a PRO verify that my suspicion is correct? Or, exactly what does this setting do? Thanks.

V

Thank you for reporting this comment. Undo
PRO
CJ Mechanical of North jersey llc.

selecting higher seer sw1#6 on position increases air flow for low stage(1 stage) . furn off and you will run 50% 1st stage then 100% 2nd stage

    Bookmark   May 8, 2012 at 8:05PM
Thank you for reporting this comment. Undo
veesubotee

Thanks Coolmen, I suspected (increase) as much. If I interpret your comment correctly, with switch on, airflow in stage 1 > 400 CFM/ton.

If so, would using a humidistat for dehu on demand (I have the new board which does dehu and 2 stage)if I decided to, in conjunction with turning #6 off risk freezing the coil?

Thanks for your input.

V

    Bookmark   May 9, 2012 at 10:11AM
Thank you for reporting this comment. Undo
PRO
CJ Mechanical of North jersey llc.

Since having 2 stage cooling I would not worry about the dehum. running low stage should do a fine job at hum removal.
I would leave # 6 off and get 400 per ton cooling 15% less low stage. mount hum stat digital in house and see how it performs.

lossing 15% low stage plus an other 15% on dip switch setting # 6 another 15% may freeze coil. page 58

just

    Bookmark   May 9, 2012 at 6:21PM
Thank you for reporting this comment. Undo
veesubotee

Thanks. As far as the stat is concerned, I'm tied into the mod stat (411) which doesn't have dehu function.

Will set switch #6 to off. Airflow is currently set at 400 CFM/ton. Will keep it at that setting (for now).

V

    Bookmark   May 10, 2012 at 10:57AM
Sign Up to comment
More Discussions
2 Stage vs 1 Stage
I am trying to decide what HVAC replacement system...
cms9323
New Bryant legacy vs 5 year old carrier infinity
My parents need a new a.c., There's is broken and probably...
David
HVAC question
I live near Charlotte NC and have a new Bryant Hybrid...
gtodd1966
Nozzle size for Oil Burner ??
I have a Slant fin oil furnace that heats my water...
big_al_41
auxiliary heat vs. emergency heat
Greetings, I have a Bryan Evoltion Control heat pump...
decadent
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™