I have a 3 ton central AC/Heating unit which uses a 20x24x1 filter. We recently put an addition, approx. 500 sq ft, on the house for a total of approx. 1500 sq ft.

We were told the existing unit was enough to support the addition. Should we make the intake vent a bit larger around 20x25x1 at least?

Thank you for reporting this comment. Undo
mike_home

The filter size is determined by the amount of air flow which must pass through it. You have to determine when the air flow is the highest between the furnace and AC. The formula I use is for a filter rated for a velocity of 300FPM:

air flow (CFM) / 2.08 CFM/sq. in. = filter area (sq. inches)

Let's assume you have a 3 ton AC which would normally be using 1200CFM of air. The filter area calculation would be:

1200CFM /2.08 CFM/sq. in.= 577 sq. in.

A 20 X 24 filter (480 sq. in.) would be too small. You would need a 24 X 25 filter. The fact you added 500 sq. ft. of area does not change the filter requirements. If you are going to change the filter then see if you can fit a 4 inch media filter. They are less restrictive and last longer than the one inch.

    Bookmark   May 20, 2013 at 10:25AM
Thank you for reporting this comment. Undo
aceh

Thanks Mike.

Would the CFM info be listed somewhere on the unit?

    Bookmark   May 20, 2013 at 12:51PM
Thank you for reporting this comment. Undo
mike_home

It is probably not listed on the unit. It may be in your furnace manual. An air flow of 350-400 CFM is what is required per ton of cooling. Usually the air flow for the air conditioning is higher unless you have an a very big furnace.

    Bookmark   May 20, 2013 at 8:54PM
Thank you for reporting this comment. Undo
aceh

Thanks again Mike.

    Bookmark   May 22, 2013 at 8:48AM
Thank you for reporting this comment. Undo
Servicetech

Chances are if they only installed one return on a 3 ton unit they also shortchanged the return ductwork. Adding a 2nd return will allow you to get the full 3 tons you paid for. Right now it is probably like most systems that only deliver 2/3's of their rated capacity.

FWIW my house is 100sqft bigger and cools with a 2 ton AC. It will keep it 75 indoors on a 100degree day.

    Bookmark   May 27, 2013 at 9:38PM
Sign Up to comment
More Discussions
Insulating floor on my raised home in Louisiana.
We recently installed solar panels on our home. We...
ktyler1320
Greenspeed, is this setup ideal/ worth it?
I am building up on my house (cape style) in Long Island...
David
auxiliary heat vs. emergency heat
Greetings, I have a Bryan Evoltion Control heat pump...
decadent
Baseboard heater thermostats
We are looking to install (2) 120v baseboard heaters...
stephja007
Floor Air Register and ductwork
In recently doing light cleaning on air registers in...
Char Holdenried
© 2015 Houzz Inc. Houzz® The new way to design your home™