Main Breaker trips - HELP !!

maverick9001May 11, 2007

Hi,

When my A/C unit runs, it trips my main circuit breaker. Not always. Its random. sometimes it trips 3 or 4 times a day. then runs fine for a day, then trips again. The breakers inside my house are not tripped. they look fine. I had to go outside my house and OFF the breaker and then turn it ON. I had called my utility company. They told me first to replace the main breaker and if it happens again then there is a problem inside the house.

Should I call a electrician first ? can I replace the main braker myself ?

Thanks.

Thank you for reporting this comment. Undo
bob_brown

I would probably inspect all electrical connections. Somewhere you either have an excessive load or a poor connection. A hot day will add to the resistence of the system. Resistence equals amps, which will cause the breaker to trip.

A compressor that is overcharged can cause the breaker to trip on a hot day. A fan motor that has a bad capacitor can cause the breaker to trip. A weak breaker can also trip. I have found poor connectors between the wire from the pole and the house feed wire to cause a voltage drop, which affects everything in the house.

Finally, if the wiring to the condenser is too small, it can cause the breaker to trip.

    Bookmark   May 11, 2007 at 1:09AM
Thank you for reporting this comment. Undo
hendricus

What else is running when the main breaker trips? Is this a new installation? How large is your electric service? Does it trip when the air is on, dryer is running, four burners and the wall oven and the vacuum and then you turn on the pinball machine?
There is either too large an electrical load or the breaker is bad.

    Bookmark   May 11, 2007 at 3:27PM
Thank you for reporting this comment. Undo
mr_havac

When was the last time you had the system serviced? Chances are its something like a plugged up condenser coil in a low end unit that doesn't have any hi or low pressure controls, or badly corroded or loose terminals. Many times the compressor terminals are overlooked when checking electrical connections and they do get loose.
If its been a while have your system serviced first before you go calling an electrician.

    Bookmark   May 11, 2007 at 3:51PM
Thank you for reporting this comment. Undo
maverick9001

Thanks for your replies...
The HVAC unit is 9 yrs old.

when the breaker tripped the microwave was running once, other time the dryer was running.. all other times it was the A/C and probably TV was running.. no other appliances were running..

I changed the breaker for HVAC (its a 30 amp breaker) and it still trips..The main breaker outside is 100 Amp.

I'm calling a HVAC contractor tommorrow for servicing. what should I ask him to check for ? are checking AMPS or leaks part of the service ?

I finished my basement last fall and also ran a seperate line for microwave(both done by a contractor). but after this I have used my heating, washer, dryer, microwave etc. simultaneously. never tripped.

thanks for your input guys..

    Bookmark   May 14, 2007 at 10:25PM
Thank you for reporting this comment. Undo
maverick9001

How much would it cost on an average to service a heating & cooling system ? I live in Central New Jersey.
Thanks..

    Bookmark   May 14, 2007 at 10:50PM
Thank you for reporting this comment. Undo
daddo

I agree- have the a/c checked out first.
The 100 amp breaker may be going bad and the stabs it connects to in the panel may be corroded some. If there is a loose connection or corroded stabs, this will overheat the breaker and sometimes slowly cook it to the point it needs replacing.

    Bookmark   May 14, 2007 at 11:05PM
Sign Up to comment
More Discussions
Why is split ductless so expensive when installed?
Hi, Long time reader, first post. I have a question,...
JHZR2
gas wont come on. forced air gas fired furnance
the Furnace was starting then running a couple minutes...
waterguytexas
Need help with selecting Eff Heat Pump replacement.
20 yr old American Std Heat Pump stopped working. ...
2015hvac
Advice on Attic insulation
So we just finished the second year in our house and...
w_fournier
Geothermal (GSHP) replacement
My almost 80-year-old mother's house was built in 1998...
DavidR
Sponsored Products
Geo Medallion Rug 8' x 11' - WHITE/ORANGE
$1,399.00 | Horchow
Eclipse Thermaback Microfiber Grommet Blackout Window Panel - 10708042X063BE
$19.99 | Hayneedle
Tibetan Beige Rectangular: 6 Ft. x 9 Ft. Rug Rug
Bellacor
"Hobson" Cube - GRAY
$900.00 | Horchow
Herman Miller | SAYL® Adjustable Work Chair
YLiving.com
Canterbury Jeffie 54x54 Inch Dining Table w/ Butterfly Leaf
Beyond Stores
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™