Possible TXV Probem fixed ?

scruffy12April 10, 2012

Have a Lennox 2.5 ton and had a problem where between cooling cycles compressor would go into overload. Installed a hard start ( a good one with time dely etc. ) and sometimes with that it would not start on the first go around.

My neighbor down the street who is a well retired disabled HVAC guy ( 89 years old ) hooked up his gauges and found that the pressures were taking about 20 minutes to equalize. This problem was on going for about a month. Freon charge was good.

( I don't have the readings we took ).

He suspected a defective TXV valve so he had me take all he insulation off the TXV bulb and found it was not securely attached to the evaporator outlet line. On inspection there was a lot of green and white stuff on the bulb and line which lookied like heavy corrosion.

I cleaned it up with a fine sandpaper making the copper on both sides shiny. He then had me apply a small amount of heat sink compound to both surfaces and remounted the TXV bulb and insulated.

Now the problems seems to be fixed..what I need to know is if the bulb was not getting the proper temperature to regulate the flow of refrigerant would this effect the valve operation. His thinking is that it may have been flooding the compressor.

Now the cooling is fantastic as it seemed over the past few months it was not cooling as good as it always done. He said to leave the hard start in as it will do no harm.

Whats you opinion on this as its been cycling fine for the past 3 days here in warm Florida.

Thank you for reporting this comment. Undo
veesubotee

Sounds like you should hold on to him.

    Bookmark   April 11, 2012 at 2:17PM
Thank you for reporting this comment. Undo
brickeyee

"if the bulb was not getting the proper temperature to regulate the flow of refrigerant would this effect the valve operation."

The temperature is what makes the valve operate.

Wrong temp, bad performance.

    Bookmark   April 11, 2012 at 3:46PM
Sign Up to comment
More Discussions
carrier infinity with greenspeed service settings
We just built a new home in central Kansas this year,...
Energywise.ks
Navian condensing combi, good or bad?
Hi, I am looking into converting from oil to gas and...
rickyk22
Heat pump choices for first timer. Advice??
Hello, First post, great place you all have here. We...
adayrider
New Mini Split Designs for 2015
I, and I am sure others, would love to hear what is...
josey11
Greenspeed, is this setup ideal/ worth it?
I am building up on my house (cape style) in Long Island...
David
© 2015 Houzz Inc. Houzz® The new way to design your home™