HVAC Comparison

kiropodApril 21, 2011

I think that I've finally narrowed my proposals down to these 2.

Lennox 97% modulating gas furnace, 66,000 btu- model SLPUH070V36B

Lennox XP 17 3.0 ton heat pump

Lennox evap coil, model cx34

lennox touch screen iaq programmable thermostat

air plenum with Merv 16 filter with uv light set up

lennnox humidifier

condensation pump,

Carrier infinity furnace model 58mvc060f114 3 stage variable speed furnace

carrier performace 16 ser dual stage condensor, model 25HPA636

carrier evap coil CNPVP3617ATA

Infinity thermostat control

infinity air purifiier

honeywell large bypass advanced humidifiers

I did have a manual J and an energy audit performed. FYI, the Carrier proposal is $8,000 more. I know by looking at the specs that the Lennox heatpump is only a 1 stage, whereas the carrier is 2 stage.

Thank you for reporting this comment. Undo
mike_home

Does the Carrier quote include the $1100 rebate? It is hard to believe the Carrier contractor wants $8000 more. Is there additional work being done?

Is the Lennox dealer proposing using a Merv 16 filter? I would be concerned about the increased static pressure. As the contractor about this. The static pressure reading should be in the 0.6-0.7 range. I am not sure if the Lennox thermostat gives this reading. I know the Infinity controller does.

    Bookmark   April 21, 2011 at 9:49AM
Thank you for reporting this comment. Undo
neohioheatpump

I would do the lennox quote. Thats nice equipment. Modulating gas furnace and xp17 heatpump are high end stuff. How much is that quote running you?

    Bookmark   April 21, 2011 at 11:01AM
Thank you for reporting this comment. Undo
kiropod

Well. I will be getting 2 of each. The Lennox will be around $20,000 after rebates and NJ credit

    Bookmark   April 21, 2011 at 11:12AM
Thank you for reporting this comment. Undo
kiropod

after crunching the numbers once again, the savings will be $4000 for the Lennox, not $8,000 Still that's a chunk of change. The Lennox had to be bumped up to an 80,000 BTU due to matching issues with the heatpump, but same price.

    Bookmark   April 21, 2011 at 2:02PM
Thank you for reporting this comment. Undo
mike_home

What were the Manual J calulations for each floor?

    Bookmark   April 21, 2011 at 2:23PM
Thank you for reporting this comment. Undo
kiropod

The manual J recommended 60,0000 BTU furnace and 3 ton AC. The Lennox contractor stated that if we go with their 3 ton heat pump we must move up from their 66,000 btu to a 80,000 btu furnace, but since its a modulating furnace, it will likely never need to use that much energy. Does this make sense?

    Bookmark   April 21, 2011 at 4:45PM
Thank you for reporting this comment. Undo
neohioheatpump

Yes, it does make sense. Sounds like a nice system. How much square footage on each floor? So you decided to go with 2 different systems rather than one system zoned I see. Thats fine. Is this a new house or existing construction?

    Bookmark   April 22, 2011 at 7:33AM
Thank you for reporting this comment. Undo
kiropod

Not sure what you mean by 2 different systems. We are going forward with the Lennox system, modulating 98% furnace and heatpump.

    Bookmark   April 22, 2011 at 9:20AM
Thank you for reporting this comment. Undo
neohioheatpump

I thought you mentioned in a previous post you would be getting 2 of each.

    Bookmark   April 22, 2011 at 9:45AM
Thank you for reporting this comment. Undo
david_cary

2 different systems - you stated you were getting 2 of each. People often do a single system and zoning controls.

It might be worth considering a single system with zoning controls. It may not really be an easy option if this is existing construction. If it is new, it still might require extra work if you are underway.

    Bookmark   April 22, 2011 at 9:51AM
Thank you for reporting this comment. Undo
kiropod

Yes, we are replacing our two furnaces (24 years old) and AC units. Its already set up for 2 zones. Thanks for your input.

    Bookmark   April 22, 2011 at 10:25AM
Thank you for reporting this comment. Undo
tigerdunes

kiropod

this is NJ location?

one of the two furnaces is going to be located in the attic?

I would not place a condensing high eff furnace in the attic.

I think dual fuel(with heat pump) is overkill with a full modulating furnace.

But if you place an 80% furnace in attic, then I would pair with high eff HP.

IMO

    Bookmark   April 22, 2011 at 12:26PM
Thank you for reporting this comment. Undo
kiropod

Both are in the basement.

    Bookmark   April 22, 2011 at 1:19PM
Thank you for reporting this comment. Undo
mike_home

Did you look at the Manual J calculation? What was the calculated sizes for heating and cooling of each floor?

If find it hard to believe you need 6 tons of cooling for your house. I am not familiar with the Lennox furnaces. I think your choices are either 70,000 or 90,000 BTU input furnaces at 97% AFUE. It seems your contractor is recommending two 90,000 units or 180,000 BTU for your house. This also seems oversized.

Are you confident this contractor knows what he is doing?

    Bookmark   April 22, 2011 at 5:23PM
Thank you for reporting this comment. Undo
kiropod

As noted before, the manual J recommended two 60,000 BTU furnaces and 2 3 ton AC's . The carrier quote (he did the manual J) included 3 stage variable speed 60,00 btu infinity 955 furnace with a 3 ton performance 16 ser dual stage compressor.

The Lennox quote is for a 90,000 btu fully modulating furnace. I did ask him about oversizing the furnace, but he said in order to match up the 3 ton heat pump, he had to jump up to the bigger furnace and since it is fully modulating, it will likely never need all 90,000 btu's. It's a large house with high cealings, etc.

    Bookmark   April 23, 2011 at 8:57AM
Thank you for reporting this comment. Undo
mike_home

Do your heat pumps qualify for the NJ Cool Advantage rebate program. They need to be at a minimum of 16 SEER, 13 EER, and HSPF 8.5. If you do you will get $500 for each heat pump. Your furnaces qualify for the $400 Warm Advantage progam. Your total rebates would be $1400 assuming the contractor will submit the applications.

    Bookmark   April 23, 2011 at 11:44AM
Thank you for reporting this comment. Undo
mike_home

Correction, the total would be $1800 for the two furnaces and heat pumps.

    Bookmark   April 23, 2011 at 12:05PM
Thank you for reporting this comment. Undo
kiropod

The heatpumps are 17 SEER, 9.5 HSPF. Yes, he is going to submit this for us. Thanks mike_home

    Bookmark   April 23, 2011 at 6:16PM
Sign Up to comment
More Discussions
Central Air OR Mini-Split
Hello everyone, We bought our house 2 years ago (1938...
Bongo
Geothermal in new construction.
Our house is currently under construction, and while...
bethmcg
company insists on all payment in advance
Having 2 mini-splits installed, have already paid half...
gramarows
Geothermal (GSHP) replacement
My almost 80-year-old mother's house was built in 1998...
DavidR
2 HVAC quotes: need to decide
I'm ignorant of HVAC, but willing to do the research...
davidarcher2
Sponsored Products
Indoor Ceiling Fans and Light: Westinghouse Industrial 56 in. Brushed Nickel Cei
$66.81 | Home Depot
DW 3528 LED Strip Light 60/m 4mm wide 5m Reel
EnvironmentalLights.com
Waterproof Green LED Neon, by the Meter
EnvironmentalLights.com
Indoor Ceiling Fans: Westinghouse Fairview 52 in. Brushed Nickel Ceiling Fan 784
Home Depot
Bruna Parede Wall Fan
Lightology
Bruna Parede Wall Fan
Lightology
Sample - Loft Seafoam Frosted 3x6 Glass Tiles 1 Piece Sample
$2.99 | TileBar
Venstar T2800 Commercial Platinum Slimline Thermostat - VST2800
$101.84 | Hayneedle
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™