How to measure BTU/hr. ?

gregteMarch 29, 2008

I have made a simple air to air heat exchanger that flows 3 CFM of air and lowers the air's temperature 10 degrees F.

As far as I can tell this means that the heat exchanger has a capacity of 135 BTU/hour. I derived this by using the following formula:

BTU/hr. = CFM * delta-T * 4.5

Is this correct?

Thanks

Thank you for reporting this comment. Undo
tom2112

The basic equation is

q = m*Cp*delta-T

where q is the heat transfer rate, m is the mass flow rate, Cp is the specific heat of air and delta-T is the temperature difference.

This equation applies to both sides of the heat exchanger, and the q's must be equal. Your equation is using CFM, which is a measure of volumetric flow rate rather than mass flow rate. To convert, use

m = Q*rho

where Q is the volumetric flow rate and rho is the density of air.

You need to keep track of the units of measurement in all of these equations. It's possible that the 4.5 factor in your equation takes care of the gas properties (specific heat and density) and the units, but I couldn't say for certain without access to my reference books (don't keep them at home!).

    Bookmark   March 29, 2008 at 8:45PM
Thank you for reporting this comment. Undo
garyg

BTU per hour = CFM x 1.08 x Delta T

The 1.08 factor gets the units straight.

    Bookmark   March 31, 2008 at 7:37AM
Thank you for reporting this comment. Undo
dan_martyn

Technically, since 1997 the Standard air calculation has been revised to accommodate for humidy. The original factor of 1.08 is for dry air.

BTUH = 60 x 0.075 (0.24 + 0.45W) x CFM x Delta T

BTUH = 4.5 x .2445 x 3 x 10

BTUH = 33

Where:
60 = min/hr
0.075 = lb(dry air)/ft3
0.24 = specific heat of dry air, btu/(lb* degrees f )
W = Humidity ratio, lb(water)/lb(dry air)
0.45 = specific heat of water vapor, btu/(lb* degrees f )

When W = 0.01 the value = 1.10
When W = 0.02 the value = 1.12
When W = 0.03 the value = 1.14

Thus, because a value of W = 0.01 approximates conditions found in many air-conditioning problems, the Sensible heat change (in btu/h) can be found as;

BTUH = 1.10 x CFM x Delta T

The preceeding was extracted from 1997 ASHRAE Handbook "Fundamentals", page 28.15.

Dan Martyn

    Bookmark   March 31, 2008 at 10:51AM
Thank you for reporting this comment. Undo
cwbig209

We've been working on computing some BTUH in different locations with different humidity ratios. When I checked the 1997 handbook which you referenced I noticed they used slightly different figures for the values. For example, you mentioned that "when W = 0.01 the value = 1.10, when W = 0.02 the value = 1.12, when W = 0.03 the value = 1.14", whereas in the handbook, it shows these values as: 1.23, 1.25 and 1.27 respectively. I wasn't sure what that difference might be and I wanted to make sure before we started in on the calculations that we were doing them correctly.

Thanks

Curtis

    Bookmark   April 6, 2009 at 1:45PM
Sign Up to comment
More Discussions
Need help choosing an efficient HRV Air Exchanger
Hi, My house as a total area of 2300 square feet (1150*x)....
Jim_Lafleur
Enery efficiency of exposed ductwork?
What are your thoughts on the energy efficiency of...
ccintx
Insulating floor on my raised home in Louisiana.
We recently installed solar panels on our home. We...
ktyler1320
Navian condensing combi, good or bad?
Hi, I am looking into converting from oil to gas and...
rickyk22
Baseboard heater thermostats
We are looking to install (2) 120v baseboard heaters...
stephja007
© 2015 Houzz Inc. Houzz® The new way to design your home™