Testing oil burner transformers & cad cells

redpondFebruary 25, 2008

In reading the Beckett burner won't keen running it was said the transformer was tested. I would like to know how you test a 12 or 14,000 volt transformer. How does one measure that much voltage. Does the voltage have to be 14,000 volts or is 9,000 volts OK ? As for testing cad cells can it be tested with a meter? And if so how???

Thank you for reporting this comment. Undo
baymee

There are meters that will test for voltage, but probably if the guy could draw a 3/4" long spark, he said it was OK.... and it was.

Cad cell eyes can be tested with an ohms meter. In the presence of light, the ohms drops to about 300-1300 ohms.

Cad cells are checked through a process of elimination.

    Bookmark   February 26, 2008 at 5:52AM
Thank you for reporting this comment. Undo
redpond

I guess what you are saying is that a transformer is a go or no go. It either has 12 or 14,000 volts or it has non.

    Bookmark   February 26, 2008 at 2:53PM
Thank you for reporting this comment. Undo
baymee

No, they can get weak. I've had alot of warranty returns of "weak ignitors". They were supposed to NOT get weak (either work or not), but Beckett has conceded that they can get weak. Transformers usually last for hundreds of years or they burn up.

    Bookmark   February 26, 2008 at 6:53PM
Thank you for reporting this comment. Undo
corvetteguy

Very Simply.
I saw the repair guy test mine.

OPEN up the igniter box and rotate it over so the springs are
pointing up, not down touching the two rods.

TURN ON the heat so the pump is running, The repair guy
disconnected the wires to the pump so he could leave
ot on for a few minutes. Otherwise only do the test
for 30 seconds so you don't fill the chambre with oil
spray.

Hold a screwdriver across the two springs holding
the insulated handle. Slowly pull the screwdriver
away from one spring and observe how far you are
able to maintain the arc.

A good coil will maintain the arc way over an inch.

Less than that and it is weak.

Note that igniters may get temp sensitive over time.
And for $35 it may be best to change it.

The photo cel will turn off the system in 40 seconds
if not exposed to brite flame ;ight.

    Bookmark   February 27, 2008 at 7:55AM
Thank you for reporting this comment. Undo
baymee

Note that it won't even start unless the eye sees no light.

    Bookmark   February 27, 2008 at 11:14AM
Thank you for reporting this comment. Undo
corvetteguy

My beckett 1a will start fine, the cad
lite kicks in on the 40 seconds if the
flame is not seen. The control module
takes care of this.

    Bookmark   February 27, 2008 at 4:46PM
Thank you for reporting this comment. Undo
baymee

Yes, the primary control will shut off the burner motor after 45 seconds on the old type and 15 seconds on the new type.

    Bookmark   February 27, 2008 at 6:14PM
Sign Up to comment
More Discussions
New Furnace - Keep Previous Excellent Thermostat?
I am replacing a 20-year-old single-stage Carrier gas...
ak0402
can people share their weekly propane use and square footage, please?
With the coldest weather in roughly 20 years here,...
davidrt28 (zone 7)
ERV Systems
Hello: Is it really safe to forego bathroom exhaust...
Dona Dinkler
Manual J -> S ->D
JSHR: 0.81 MJ8 Tons: 3.03 SqFt/Ton: 1667 CFM/SqFt:...
Brian S
Pls tell me the best uses for Carrier Air Handler Model # FV4CNF003
Hi GW, I am stuck with a new 2012 air handler/heat...
ontariomom
© 2015 Houzz Inc. Houzz® The new way to design your home™