Venting experts: Does this seem OK to you?

ginny20August 5, 2012

When we redid the kitchen last year it turned out that, due various factors, the only way to vent to the outside was to go in the wall, down to the basement, across the basement ceiling, then out. I thought this was pretty ingenious of the GC. I understand that a run this long and with so many turns isn't optimal, but my hood seems to draw well anyway.

But when I run it, I notice that the basement smells like whatever I'm cooking. This suggests to me that the duct work isn't completely sealed. (Another possibility is that the vent outside is near the cellar door or window, and the smell is getting back in that way. But the basement doesn't smell like smoke when we grill out there, so I think that's less likely.) DH says it's virtually impossible to seal ducts enough so there is no leak. So do you think I have a problem or not?

Thank you for reporting this comment. Undo
PRO
Sophie Wheeler

Yes, you have a problem. The design is pretty sub optimal to begin with and needs to be checked to make sure the CFM are adequate for such a long twisty run as well as the ductwork is large enough. Then the ductwork needs to be inspected at the joins as well as the exit location. Was this inspected by a codes enforcement inspector from your municipality?

    Bookmark   August 5, 2012 at 11:54AM
Thank you for reporting this comment. Undo
ginny20

I have plenty of cfm - it started at 800, and it's only induction. It sucks like crazy and I don't even run it on high. The ductwork is 10". But I do wonder about whether it's leaking at the joints.

I don't think anyone actually has a code enforcement inspection on remodels around here, unless you're actually building out new foundation.

    Bookmark   August 5, 2012 at 9:06PM
Thank you for reporting this comment. Undo
kaseki

Try using metal-based duct tape [not duck or gaffer tape] around all the joints.

kas

    Bookmark   August 6, 2012 at 9:10AM
Thank you for reporting this comment. Undo
weedmeister

an HVAC guy might suggest mastic for the joints.

I'll also wager you did not install any MakeUp Air. This would mean that as you run the fan there is negative pressure inside your house. The exhaust is probably finding it's way back into the basement through door or some other leakage point.

    Bookmark   August 6, 2012 at 4:20PM
Thank you for reporting this comment. Undo
ginny20

No, you're right,we don't do MUA around here. But the house is old and very far from air tight. There's a keyhole (for an old skeleton key) in the door to the garage maybe 6 ft away from the hood, and you can see right through it. I know air comes in that way, plus around that door. Your suggestion is possible, though. We have one of those old fashioned cellar doors right next to where the exhaust comes out, so it could be coming back in there. That wouldn't bother me as much as if the duct isn't sealed.

I'll see what the joints are sealed with. My GC was not an HVAC guy, and I may need one to get this right.

Thanks for all your suggestions.

    Bookmark   August 6, 2012 at 11:37PM
Sign Up to comment
More Discussions
Need A New Keurig - Suggestions?
Our Keurig at the lake bit the dust. The single cup...
amck2
High end appliances thermador vs. dacor
I currently have dacor ovens. I am trying decide brands...
mcaprizs
What electric oven to get? speed oven, combo-steam, or regular?
If I am going to go with an all gas range, which would...
nismo99
Wolf oven error on self clean: TCO detect as open
I've had two Wolf E series for nearly 2 years (single...
repac
36" Blue star range- tight on space and can't decide on one electric o
Doing a kitchen renovation and have space for a 36"...
nismo99
People viewed this after searching for:
© 2015 Houzz Inc. Houzz® The new way to design your home™